OK so most of my 30 year experience with HVAC has been in large commercial AC units so this little Tecumseh AEA4440AXA R-12 under counter hi temp refer box has got me stumped. Unit pulls down, satisfies & shuts down fine. Off cycle duration is about 12 - 20 minutes. When stat calls for cooling compressor wont start (cuts out on klixon protection) until the HI - LO press differential is less than 22 psi. Compressor is new & all windings ohm out good, changed overload, start relay & capacitor with no change. By the time compressor is able to start the box temp is too warm. My question is this: With these small high torque compressors, what is the typical HI - LO pressure differential compressors can overcome @ start? Thanks Guys!!
Jim
-
01-24-2013, 04:06 PM #2
I would suggest calling tecumseh for the exact pressure but to me that sounds typical at 20 -30 psig. I'm thinking partially restricted cap tube due your pressure should have equalized within the 12-20 minutes off cycle. I can't say that for sure but seems to me.
Joe S.
-
01-24-2013, 06:28 PM #3
Regular Guest
- Join Date
- Jun 2003
- Location
- Tampa Bay, FL.
- Posts
- 119
12 minutes is plenty of time for that unit to equalize. I would suspect a restriction also. What are your pressures?
-
01-24-2013, 07:16 PM #4
Professional Member
- Join Date
- Jun 2003
- Posts
- 3,658
The high torque models can easily start against a 200 psi differential. They don't need any equalizing time.
What is the supply voltage while it is attempting to start?
-
01-25-2013, 05:17 AM #5
Heres the tech sheet for that pump.
http://www.tecumseh.com/en/united-st...?pdf=datasheet
Whats the SH when running?
-
01-26-2013, 02:39 PM #6
Regular Guest
- Join Date
- Sep 2007
- Location
- British Columbia
- Posts
- 12
This unit isn't on an extension cord or anything like that is it?? that will create a voltage drop...
-
01-27-2013, 09:57 PM #7
Make sure it's on it's own circuit,worked for coca cola for years,had them baby's all plugged in along with Pepsi coolers and what not,that's a 1/2 hp compressor any kind of voltage drop will cause that.
if at first you dont succeed,then skydiving is not for you
-
01-28-2013, 07:27 AM #8
Regular Guest
- Join Date
- Jun 2003
- Location
- Tampa Bay, FL.
- Posts
- 119
We need more details. Is this a single door or multiple door cooler? Model? Manufacturer? Etc.
-