Thread: Jace 6 or 7?
    Jul 2010
    Denver, CO
    Jace 6 or 7?
    I am trying to decide which Jace to go with and need some help deciding.
    I will be controlling 18 AI, 10 AO, 18 BO, and 15 BI through logic on the jace. Besides that I will be importing points from 2 boilers and a chiller over MS/TP.
    The real reason I'm considering the 700 though is that I will have 35 EasyIO 30P's, which are stand alone controllers. Each one controlling an air handler. I will be importing all these points into the Jace through Sedona and have graphics for them all. I don't know how much RAM it will take to keep up with all communications.
    What is your guys thoughts on this?
    Melbourne
    if yr using Bacnet IP for the EasyIOs then gut-feeling says a 600 should romp it in.
    if yr doing MSTP then ...er...maybe not...depends
    1 + 1 = 3 ( *** for very large values of 1)
    ...everybody wants a box of chocolates and long stemmed rose
    Be brave. You cannot get eaten by an imaginary tiger.
    Jul 2010
    Denver, CO
    I will be using tcom to communicate with the 30P's which is the essentially using Sedona, this way every point is accessible in the Jace. I will also be eliminating all NDIO/NRIO and moving everything to 30P's so the chiller and boiler plants will be standalone.
    Does anyone have experience with a large system like this?
    Melbourne
    Quote Originally Posted by HuNGRYTeCH View Post
    ...be safe then and use a 700
    yes, actually we are doing one the same size right now and using a 700.
    This will run bacnet, Lon and modbus concurrently
    typically we use bacnet simply because the overrides work better.