    http://www.facebook.com/video/video....ideo_processed[/video]

    had this one last night. inlet pressure is 6.9 and outlet pressure is 3.45. i cleaned the burners but the only one dirty was the first one that is rolling back at start up. cleaned orifices. still has roll back at start up. i did notice when i was turning the furnace on and off to check it, that if i didnt let the inducer completely stop before turning it back on it wouldnt have roll out. what do yall think?

  2. #2
    Join Date
    Jun 2012
    Location
    Rising Sun, Maryland, United States
    Posts
    111
    Post Likes
    did you inspect the heat exchanger?

  3. #3
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    did you clean the pilot orafice ?

    its like the gas valve is opening too slow

    can you swap burners around ??

  4. #4
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    check the amp draw on inducer fan motor.

  5. #5
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    872
    Post Likes
    Thread Starter
    Amp draw was .9 name plate 1.7

  6. #6
    Join Date
    Oct 2011
    Location
    Toronto
    Posts
    40
    Post Likes
    That is strange, make sure to share the outcome. Never know when youll come across something like this

  7. #7
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    872
    Post Likes
    Thread Starter
    I do remember the valve took about 2 or 3seconds to get to 3.45. Is that normal or is it usually immediate

  8. #8
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    I believe I heard they do make valves that are slow openers , i dont know enough about them to tell you anything , but if one got installed into that furnace on accident , it will act similar to what you are seeing

    If the pilot flame is Not big enough it could do that , or make a Whoosh sound

    Some are a real pain to diagnose

  9. #9
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Delayed ignition. Check the runners on the burners. Make sure they are spaced enough. Was the valve replaced?

  10. #10
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Let the furnace run for 5 minutes. Turn off gas valve, let flame go out, turn it right back on and see if it lights normal

  11. #11
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Quote Originally Posted by gravity View Post
    Let the furnace run for 5 minutes. Turn off gas valve, let flame go out, turn it right back on and see if it lights normal
    ahh .... you are bypassing the valve this way , checking to see if valve is opening too slow , good idea !

  12. #12
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    872
    Post Likes
    Thread Starter
    valve was not replaced. it was original

  13. #13
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    872
    Post Likes
    Thread Starter
    it will light normal because the inducer i still running. it lights normal when i cut the switch off and back on before the inducer has time to completely stop.

  14. #14
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    pull the flue pipe off and try it from a dead stop and then while its running. check the runners and make sure they are clean.

    check the manifold. there could be lots of spiderwebs in it.

  15. #15
    Join Date
    Jan 2015
    Location
    Bellevue, Washington, United States
    Posts
    2,388
    Post Likes
    Sounds like a cracked heat exchanger.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •