    had this one last night. inlet pressure is 6.9 and outlet pressure is 3.45. i cleaned the burners but the only one dirty was the first one that is rolling back at start up. cleaned orifices. still has roll back at start up. i did notice when i was turning the furnace on and off to check it, that if i didnt let the inducer completely stop before turning it back on it wouldnt have roll out. what do yall think?

  2. #2
    Join Date
    Jun 2012
    Location
    Rising Sun, Maryland, United States
    Posts
    111
    Post Likes
    did you inspect the heat exchanger?

  3. #3
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    4,818
    Post Likes
    did you clean the pilot orafice ?

    its like the gas valve is opening too slow

    can you swap burners around ??

  4. #4
    Join Date
    Aug 2012
    Posts
    3,947
    Post Likes
    check the amp draw on inducer fan motor.
    It's not if your doing it right it's whether your doing the right thing that is important.

  5. #5
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    638
    Post Likes
    Thread Starter
    Amp draw was .9 name plate 1.7

  6. #6
    Join Date
    Oct 2011
    Location
    Toronto
    Posts
    40
    Post Likes
    That is strange, make sure to share the outcome. Never know when youll come across something like this

  7. #7
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    638
    Post Likes
    Thread Starter
    I do remember the valve took about 2 or 3seconds to get to 3.45. Is that normal or is it usually immediate

  8. #8
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    4,818
    Post Likes
    I believe I heard they do make valves that are slow openers , i dont know enough about them to tell you anything , but if one got installed into that furnace on accident , it will act similar to what you are seeing

    If the pilot flame is Not big enough it could do that , or make a Whoosh sound

    Some are a real pain to diagnose

  9. #9
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,309
    Post Likes
    Delayed ignition. Check the runners on the burners. Make sure they are spaced enough. Was the valve replaced?

  10. #10
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,309
    Post Likes
    Let the furnace run for 5 minutes. Turn off gas valve, let flame go out, turn it right back on and see if it lights normal

  11. #11
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    4,818
    Post Likes
    Quote Originally Posted by gravity View Post
    Let the furnace run for 5 minutes. Turn off gas valve, let flame go out, turn it right back on and see if it lights normal
    ahh .... you are bypassing the valve this way , checking to see if valve is opening too slow , good idea !

  12. #12
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    638
    Post Likes
    Thread Starter
    valve was not replaced. it was original

  13. #13
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    638
    Post Likes
    Thread Starter
    it will light normal because the inducer i still running. it lights normal when i cut the switch off and back on before the inducer has time to completely stop.