Auxiliary lockout temperature
I'm trying to learn how to adjust our heat pump's auxiliary lockout temperature. Please, any assistance would be fabulous because it seems to be set pretty high...
thanks!
amber
-
01-23-2013, 10:26 PM #2
Then you would need to post the brand and model number of your hemostat and heat pump.
-
01-24-2013, 07:23 AM #3
Professional Member*
- Join Date
- Jul 2010
- Location
- nebraska
- Posts
- 1,165
Also post if the back up heat is gas,oil or electric and what your utility rates are.
-
01-25-2013, 01:03 AM #4
Regular Guest
- Join Date
- Jan 2013
- Posts
- 6
its a goodman heat pump, i do not know the model (i was poking around the box outisde and in the basement)
we have a Honeywell thermostat TH6320U1000
our backup heat is electric. its all electric...
-
01-25-2013, 01:14 AM #5
Regular Guest
- Join Date
- Jan 2013
- Posts
- 6
7.544 cents per kilowatt is our electric rate
-
01-25-2013, 02:13 AM #6
That thermostat is not capable of locking out auxiliary heat on its own. Depending on how your system is wired there may be an outdoor thermostat installed at, near, or inside of the heat pump.
Keep in mind that sometimes people will disconnect auxiliary heat altogether to save money.
-
01-25-2013, 02:35 AM #7
Regular Guest
- Join Date
- Jan 2013
- Posts
- 6
how can i disconnect the auxiliary heat? will it damage the system? I live in Pennsylvania and our winter is checking in at 14 degrees f... what do i need to look for when looking for an outdoor thermostat?
-
01-25-2013, 05:23 AM #8
You don't want to disconnect your aux heat. unless you want your house temp to drop.
-
01-25-2013, 07:38 AM #9
Regular Guest
- Join Date
- Jan 2013
- Posts
- 6
okay then. how do I lower the lockout temperature?
-
01-25-2013, 08:09 AM #10
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
01-25-2013, 07:19 PM #11
I would not disconnect the aux. heat either. With the temps you have in your area you will need it when the heat pump goes into defrost to keep up with the heating demand.
As others have said you first need to know if your t-stat is capable of locking out the heat pump! If not you would need to have it replaced with one that does. In my area (which does not have the cold weather) like yours we never lockout heat pump their is no need as we have very mild winters.
To be honest on my system I have only seen aux. heat come on twice this year and it has gotten to 27 here in Lousiana which is cold for us! Why are you trying to adjust it? Is it current set up bothering your comfort?
-
01-25-2013, 07:24 PM #12
-
01-25-2013, 07:30 PM #13
You will always want aux heat and never want to lock it out. It should be set up so that when you desire more than 1-2 degrees more than set point your thermostat, aux heat will run simultaneously with the heat pump. Your aux heat should also come on when the outdoor unit goes into its defrost cycle. If you lock out your aux heat al low temps your house will not stay warm. It comes on because your heat pump cannot keep up with the load.
...