    blowing fuse after awhile

    Customer has Trane heat pump that keeps blowing 5A fuse after 1-14 days.It only goes in first stage heat.I had them run emergency heat to try to blow fuse but didnt happen.

  2. #2
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    Voltage spikes may cause this, or their has to be a short somewhere in the 24volt circuit, you have to chase it down, inspect every wire.

  3. #3
    Join Date
    Jan 2008
    Location
    Texas
    Posts
    7,957
    Post Likes
    You could check amp draw also. I recently had one that was exactly like your situation. It wpuld work fine then kick a fuse. Checked tstat wire for continuity to ground and to each other. Got a quick reading a couple of times but went away. I had a good meter and set on a sensitive setting so I just thought it was picking up me touching the leads. Finally changed wire and that fixed it. Pulled some of the old wire and the insulation was brittle and the wire was green and corroded.

  4. #4
    Join Date
    Dec 2012
    Location
    Nashville, TN
    Posts
    98
    Post Likes
    Quote Originally Posted by fliks View Post
    You could check amp draw also. I recently had one that was exactly like your situation. It wpuld work fine then kick a fuse. Checked tstat wire for continuity to ground and to each other. Got a quick reading a couple of times but went away. I had a good meter and set on a sensitive setting so I just thought it was picking up me touching the leads. Finally changed wire and that fixed it. Pulled some of the old wire and the insulation was brittle and the wire was green and corroded.
    +1

    A couple of trouble spots to check for control wire breaches are where the control wire goes through the wall with the refrigerant line set and inside the compressor compartment. I can't tell you how many times I have repaired spots in the reversing valve wire or pressure switch wire where it had been resting on one of the copper pipes and time and vibration wore through the insulation creating a short to ground.

    -Brian

  5. #5
    Join Date
    Mar 2001
    Location
    Ilwaco, Washington
    Posts
    1,638
    Post Likes
    Quote Originally Posted by HighlandThunder View Post
    +1

    A couple of trouble spots to check for control wire breaches are where the control wire goes through the wall with the refrigerant line set and inside the compressor compartment. I can't tell you how many times I have repaired spots in the reversing valve wire or pressure switch wire where it had been resting on one of the copper pipes and time and vibration wore through the insulation creating a short to ground.

    -Brian
    +1
    One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •