01-27-2013, 07:32 PM #27
Regular Guest
- Join Date
- Oct 2009
- Location
- new jersey
- Posts
- 214
Im old enough to have worked on that control 20 plus years ago. The purpose of the heater in the fan control is when you start up heat in morning with cold ra temp the fan control will cool off enough to stop fan.the heater keeps the fan on with a w call
-
01-27-2013, 09:40 PM #28
Professional Member
- Join Date
- Nov 2008
- Location
- Northern California, foothills.
- Posts
- 182
After reading all of this, I'm left wondering how other furnaces using
the more common, no-heater fan/limit don't have short-cycling on
occasion. But it also makes it more clear why everybody now uses
timed fan-on, fan-off.
-
01-27-2013, 10:29 PM #29
Professional Member
- Join Date
- Jan 2009
- Location
- Salisbury, Maryland
- Posts
- 85
A pic of it would be great. At first I thought you were talking about one of the fan limits with an adjustable high limit, fan on and off tab that rotate when the HX gets warm but now I'm not sure. Either way, I'd do like T52 and check the temp at the limit and check your airflow. Its possible it could be bad but I'd confirm first because its not exactly common. You don't want to install a new one and have the same problem ya know.
-
01-27-2013, 10:33 PM #30
Professional Member
- Join Date
- Jan 2009
- Location
- Salisbury, Maryland
- Posts
- 85
Nevermind, I didn't realize so many people had posted, and with pics....... lol Anyways, seems like alot of mobile home units with gas or oil use them. Some I've noticed get "hung up" when rotating and don't always turn blower on at right time. I'm guessing because someone in the past had screwed with the dial and got it out of whack?
-
01-29-2013, 08:32 PM #31
Professional Member
- Join Date
- Feb 2004
- Posts
- 2,403
Nobody has mentioned energizing the tstat and have the blower come on after a few seconds when the gas is off. That is a sure indication there is a "heat assist" fan switch (control) installed.
-
01-29-2013, 11:30 PM #32
Professional Member*
- Join Date
- Nov 2001
- Location
- east kansas
- Posts
- 7,971
Most furnaces with these fan & limits are close to 20 years old and older. One should check the heat exchanger closely.
Beware of advice given by some guy on the Internet.
-
01-30-2013, 12:28 AM #33
No that's just a really common failure on the fan/limit combos. They get weak over time from rotating and can't push through the set point or snap back through it(so the fan either won't come on or won't turn off), don't try to wd-40 or oil them because it doesn't help, the metal is just fatigued.


Reply With Quote