  1. #14
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    2,997
    Oh I just notice the Pic. Why does you manometer say 3.5? is that with or with out the pilot light?
    Gotta have the right tool for the job!

    Where is all the stuff MADE IN THE USA?

    "Thats what we do Troy. Incredible, Invisible, Imbelivable things. We are an Unseen, Unknown, Unvincible fraternity of craftsman.."

  2. #15
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    1,375
    By the time I snapped the picture the pilot solenoid was closed and all I got was 0, I removed the small piece of tubing that connects the pilot tube to the air flow switch.
    is the oil side active?

  3. #16
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    2,997
    No it's not

  4. #17
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    1,375
    Was the burner doing the same thing before you replaced the old control? if the pilot flame signal is strong and the failure happens every now and then chances are the ignition transformer is going bad.

  5. #18
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    2,997
    Yes. I replaced the control to determine what stage the burner was failing... That's when I found it was ptfi.

    I stayed at the job late one night this week ( i forget what day, im working now from 6 this morning!) watching this thing run. Although it did not fail the incoming gas pressure to the building dropped. I couldn't get enough pressure so utility comp came out and made adjustment to the regulator.

    I'm still not out of the woods yet though. I have to adjust the burner a little and check a valve for a possible restriction. So we're getting close to the answer. I'll fill you in when I know for sure. Thanks

  6. #19
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    1,375
    any updates?

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event