  1. #1
    Join Date
    Jan 2009
    Posts
    5
    Post Likes

    Amana 80% problems

    I went on this furnace 2 times today. Arrived both times to lockout and no diagnostic lights on the board. I reset power and the furnace fires up and runs ok. Homeowner tells me ignitor comes on and gas valve comes on but does not ignite burner. I checked output gas pressure 3.5in wc. burners are clean, and placement of ignitor is positioned correctly. I just wanted to know if their could be something in the manifold as far as debris that might cause the failed ignition.I was told that the gas valve and board were replaced last year. I am going to take the gas line and manifold off and look for any debris. I was just wondering if anyone has had a similar problem to this. Thanks

  2. #2
    Join Date
    Jan 2011
    Location
    Boston, MA
    Posts
    462
    Post Likes
    Make sure igniter is the correct one for the unit

  3. #3
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    I bet you run it with the door off, and the homeowner checks it with the door on.

    Check your HX, and make some the igniter is getting hot enough to ignite. "glows" doesn't ALWAYS mean hot enough.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  4. #4
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    test resistance on ingnitor when its not hot. What kind is it?

  5. #5
    Join Date
    Dec 2010
    Location
    WV
    Posts
    405
    Post Likes
    Check for blocked flue..i.e.-birds nest, bees nest, ice, incorrect vent termination, wind blowing back into flue. Really need so more information...whats the model #, draft induced or natural draft? Vertical or horizontal? Attic or basement? what tstat is installed? have you been there when it misfires? advise the HO to stop turning it off before you get there or show them how to read the code, some boards will recycle after a set time 30mins or 60mins(once again model# will help us help u)....i am betting its a pressure switch problem...

  6. #6
    Join Date
    Dec 2011
    Location
    Twin Cities Minnesota
    Posts
    532
    Post Likes
    I had "2" this year do same...,bring out the "Torch" if it lites with this its the HSI.,alignment..,combustion air issue.

  7. #7
    Join Date
    Jan 2013
    Location
    Texas
    Posts
    33
    Post Likes
    I ran into one that was giving me problems like this and I eventually found that the gas pressure on the inlet side was not consistent, it would test just fine 70% of the time and then it would drop ever so often, it was a propane tank regulator though idk if you would have the same problem with natural gas but if there is a regulator anywhere it might pay to check it.

  8. #8
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    Quote Originally Posted by Cosmicmuffin View Post
    I had "2" this year do same...,bring out the "Torch" if it lites with this its the HSI.,alignment..,combustion air issue.
    yikes.

  9. #9
    Join Date
    Apr 2012
    Location
    Cleveland
    Posts
    744
    Post Likes
    I've had a couple do this also and it was the ignitor both times.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •