Thread: Modine unit heater?

  1. #21
    Join Date
    Jul 2007
    Posts
    76
    Post Likes
    Thread Starter
    Got back to unit today, and traced all wireing. Traced wireing from fan delay and found coil on delay h1 and h2 were wired one to tr on gas valve and the other to tr-th(coil) on gas valve. moved this over to th on gas valve and unit worked correctly. Unit was working properly in the sense that limit would open and start the fan and shut off gas as a safety but it never had proper power to fan relay coil to start fan, in this case 20 seconds after burner started. I was told this unit worked by co-worker when he did his heat inspections, but now I dont think that was the case. I guess I did not think outside the box when my assumption was that this unit was in good running order and that well it must be wired right if someone said it was working when they last touched it. When is the th-tr coil used on a gas valve when you have tr and th terminals to power your circuit through?

  2. #22
    Join Date
    Mar 2001
    Location
    Ilwaco, Washington
    Posts
    1,638
    Post Likes
    Used as a common lug on the valve
    One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •