    Honeywell q7230a 1005 interface module setup and adjustment

    Had to replace an interface module on a honeywell mod. motor and when i tryed to adjust the Zero setting i can turn the pot. all the way and the motor will not move. Not sure if i am missing something, has anyone had this problem before. The instruction say turn the zero pot all the way clockwise and the span pot all the way conterclockwise. the send closing signal (0v) turn zero pot conter clockwise untill motor starts to move then turn it back untill it stops moving. I can turn it all the way conterclockwise and the motor does not budge. Motor test out find. Used a pot can control it all the way from closed to open with out a problem. If i turn the span pot all the way clockwise and then turn the zero pot. I can get the motor to move. Any chance the instruction are wrong?

  2. #2
    Join Date
    Apr 2007
    Location
    Central PA
    Posts
    52
    Might have answered my own question but i will have to wait untill tonight to check it out. I think i need to send two volts to the module to zero it. I was using the span that someone put in our automation system and if there is one thing i should have learn by now is it is probley wrong. The interface module use a 2-10v signal we are sending a 0-10 so if this solves my problem looks like i have to change some programming also.

  3. #3
    Join Date
    Feb 2013
    Location
    Phoenix, AZ
    Posts
    198
    Yup, the module is looking for either 4-20ma (on the I+ terminal) or 2-10V (on V+).

    Dan

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event