did any one check to see if the coil is feeding 100%? such as a possible clogged distributor tube. I would want to compare pressures at coil versus outdoor unit. even though it may be airflow related don't assume it can't be a problem in side the coil, freon lines and so on. also verify the unit has the right compressor in it.