    Quote Originally Posted by crmont View Post
    Nope. Take that off the list.
    Why?

    A bad txv at the outside unit can cause high head pressure just like he's seeing & still work fine in cooling. We haven't been given any SH, SC or even suction pressure measurements so that leaves a few possibilities besides just air flow until we get them.
    Gary
    -----------
    http://www.oceanhvac.com
    An engineer designs what he would never work on.
    A technician works on what he would never design.

  2. #119
    Join Date
    Jul 2009
    Location
    South Carolina
    Posts
    2,094
    Quote Originally Posted by THPRE View Post
    Gary - I have had supposed experts out -- I should not say supposed - they impressed me with their knowledge and equiptment. The problem was that Goodman would not discuss much with anyone except the original installer. The only thing they would do was to verify that the units should work together. So if I want any warranty I have to go through things with my original installer. Thus the phone conferences. And since they just stonewall me I'm on this site to gain knowledge. And I am learning form all these answers. So Thanks to all! THPRE
    You should not have to use the original installer to do the warranty on any Goodman equipment. As long as you use a licensed HVAC contractor there shouldn't be any problem with Goodman honoring the parts warranty. I do warranty on Goodman units all the time that I didn't install. Goodman is the easiest of any manufacturer I've ever dealt with to get warranty parts from so I don't understand why you're having such a hard time finding anyone who can handle any warranty on your equipment. Now if you're talking about a labor warranty or a part that failed because of improper installation that's a different story.
    Gary
    -----------
    http://www.oceanhvac.com
    An engineer designs what he would never work on.
    A technician works on what he would never design.

  3. #120
    Join Date
    Oct 2005
    Location
    Pacific Northwest
    Posts
    1,874
    Quote Originally Posted by garyed View Post
    Why?

    A bad txv at the outside unit can cause high head pressure.....
    Because it's very rare and easily diagnosed.

  4. #121
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    1,616
    Quote Originally Posted by THPRE View Post
    OK I go for that. But the air flow in the house seems suficient. Warms the house quickly enough. It is moving enough air to cause the inner door to be forced open. It is always left open anyway. I don't have the numbers from the tests here so will look at home again. Thanks , THPRE
    ... which door are you saying is being forced?
    it's very simple. a 4 ton heat pump needs 1600cfm of airflow. that's air moving across the coil. if the ductwork is not sized properly to PERFECTLY flow air throughout the house, NOT ADEQUATELY, but PERFECTLY the VS blower will just spin faster, and faster in it's attempt to get the air to move across it. and no matter how hard you blow into a coke bottle, the air won't flow unless you give it a path large enough...
    2500 square feet should have at LEAST 2 returns with filters in them, with ducts large enough to flow the air at a low enough pressure to allow it to move with the blower provided.

    you mention 3 16" ducts feeding the 3 sections of in floor ductwork... what size is the duct the 16"ers are connected to on each end?
    The TRUE highest cost system is the system not installed properly...
    The three big summer hearththrobs...
    Mel Gibson
    Dwane Johnson
    The A/C repairman

  5. #122
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    1,616
    PRESSURE and AIRFLOW are not the same...
    a home blower is designed ONLY for a certain amount of pressure, and if the airflow at that pressure is too low, you do not get a functional SYSTEM.
    The TRUE highest cost system is the system not installed properly...
    The three big summer hearththrobs...
    Mel Gibson
    Dwane Johnson
    The A/C repairman

  6. #123
    Join Date
    Jan 2013
    Location
    TRAIL,OREGON
    Posts
    68
    The inside tx valve has been replaced twice and the outside one once.Also the drier but not the reciever. I think the suction was at 180 but I was fixated on the 610 high side. None of the changes to mechanical components or changes to the air flow have made any difference to the functioning of the refergeration system - except of course taking refergerant out and adding it back next season. Air flow changes of course made the house warm up or cool down more quickly and allowed the heat pump to run less. But the basic problem has remained the same.

  7. #124
    Join Date
    Jul 2009
    Location
    South Carolina
    Posts
    2,094
    Quote Originally Posted by crmont View Post
    Because it's very rare and easily diagnosed.
    Easily diagnosed for you maybe but that doesn't mean it would be for whoever is working on this unit. They've already changed the indoor TXV twice trying to fix this problem when supposedly the cooling was working fine. Something just doesn't add up here so I wouldn't assume anything at this point. I just saw the OP's post about the suction at 180 psi. If that's correct then it would have to be either overcharged, not enough air over the indoor coil or the coil is too small.
    Last edited by garyed; 01-30-2013 at 10:17 AM. Reason: new info
    Gary
    -----------
    http://www.oceanhvac.com
    An engineer designs what he would never work on.
    A technician works on what he would never design.

  8. #125
    Join Date
    Jan 2013
    Location
    TRAIL,OREGON
    Posts
    68
    I am already paying out for labor for all the testing and checking , I would be happy enough to pay labor to have it fixed. Maybe Goodman was just saying they would only gaurantee labor with the original installer. I know for sure that Goodman told me they would only deal with the original installer. That was in response to a phone call and an internet inquiry.

  9. #126
    Join Date
    Jan 2013
    Location
    TRAIL,OREGON
    Posts
    68
    VSTEC; I was not very specific on the door bit. Picture a rectangular room with a door at each end and the air handler in an inclosure on one side. One door to the outside and one door to the inside of the house. The inside door is what I was refering to. It is a normal 36 in door with a louvered grill in the bottom half of the dooor. This door fights being closed when the fan is running. The outside door does the same thing. I do not know the size of the three main trunks that the soft ducts are connected to. they are steel and rectangular but I don't know thwe dimensions. I guess I could cut another opening in the cabinet above the air handler and add another filter and grill. But with .05 as a max. static pressure in the return area is that needed? That was a maximum - with the out side vent in the top of the closet open it is less so the .30 total static pressures I mentioned are the highes experienced not the lowest. Thanks,THPRE

  10. #127
    Join Date
    Oct 2005
    Location
    Pacific Northwest
    Posts
    1,874
    The outdoor txv has been replaced and was never the problem anyway.

    I'm still waiting for a picture of the coil section of the air handler. I still think the coil is 90 degrees off.

  11. #128
    Join Date
    Jan 2013
    Location
    TRAIL,OREGON
    Posts
    68
    CRMONT; I am sorry about the pictures. The tx valve does fit in the cabinet and is normally closed and out of sight. The air handler is not square , it is 24 3/4 by 21 1/2 so it would be noticable if it were 90 degrees off. I'm not at home today so can't take better pictures.

  12. #129
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    1,616
    Quote Originally Posted by THPRE View Post
    VSTEC; I was not very specific on the door bit. Picture a rectangular room with a door at each end and the air handler in an inclosure on one side. One door to the outside and one door to the inside of the house. The inside door is what I was refering to. It is a normal 36 in door with a louvered grill in the bottom half of the dooor. This door fights being closed when the fan is running. The outside door does the same thing. I do not know the size of the three main trunks that the soft ducts are connected to. they are steel and rectangular but I don't know thwe dimensions. I guess I could cut another opening in the cabinet above the air handler and add another filter and grill. But with .05 as a max. static pressure in the return area is that needed? That was a maximum - with the out side vent in the top of the closet open it is less so the .30 total static pressures I mentioned are the highes experienced not the lowest. Thanks,THPRE
    where are you getting this .05 max return static number from?
    The TRUE highest cost system is the system not installed properly...
    The three big summer hearththrobs...
    Mel Gibson
    Dwane Johnson
    The A/C repairman

  13. #130
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,201
    Quote Originally Posted by vstech View Post
    where are you getting this .05 max return static number from?
    I think by taking it improperly.
    Contractor locator map