    Trane univent discharge air sensor location

    We have over 100 trane univents that they used an averaging sensor for the discharge air. The coil is about 4 inches below the sensor and the bypass is behind the coil so when we bypass the coil we still get alot of heat on the sensor so we get a lot of complaints about blowing cold air since the unit thinks it is blowing warmer air.
    Anyone seen this before? Any sugestion on how to fix it?
    Sorry I hope you understand what I am talking about. Thanks

  2. #2
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    956
    move the sensor before the bypass.

    Is there a damper after the coil and what are the settings Min/max cfm settings.

    how does the BP work, off of static pressure? do you know whats pressure it opening on. ?

  3. #3
    Join Date
    Apr 2007
    Location
    Central PA
    Posts
    51
    The units have a face and by pass coil that is how they control the discharge air temp.

  4. #4
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    956
    supply a model#

    Is this for a school?

  5. #5
    Join Date
    Apr 2007
    Location
    Central PA
    Posts
    51
    Yes this is for a school I will have to wait until tonight to get a model number I only have the control as builts nothing on the unit itself.

  6. #6
    Join Date
    Apr 2007
    Location
    Central PA
    Posts
    51
    I finaly got the model number. they are trane model vvuve100 they have one coil (2pipe system) with a face and bypass damper. There is no control of the water flow they coil is always hot. when looking down throught the grill on top of the unit you can see the coil it is at a 45 degree angle and takes up about 2/3 of the grill space and the by pass is behind the coil. the discharge sensor is an averaging type that zig zags just under the grill about 4 inches above the coil and bypass damper. So when you fully bypass the coil only half of the sensor is in the discharge air and the other half is getting radiant heat from the coil.

    Has any one ran into this before. My discharge temps are always wrong. we get lots of cold )55 degree)air blowing out of the unit even though i am reading 65-70 on the computer.

  7. #7
    Join Date
    Jun 2013
    Posts
    31

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event