    Hello,
    Had a service call today, a 2 Door Display Cooler had been tripping the breaker. I took an amp reading and found it to be drawing 12.5 amps, the name plate rating is 11.1 amps. The unit cools and everything seems mechanically sound except it trips the breaker every few days. The customer had the breaker replaced but it still happens. Any suggestions? I hate intermittent problems!
    Jul 2012
    Everett, WA
    Sounds like a ice machine we have at one of the stores, it would run fine for a while then trip the breaker, we replaced the compressor and the problem went away
    Quote Originally Posted by SurreyStevo View Post
    Hello,
    Southeastern Pa
    Hello,
    My first thought is to check the start components, particularly the relay contacts. You may not be getting full assist on a restart under load.
    Second, what size breaker are we talking about? You can only load a breaker to 80% of its nameplate rating, so a 15 amp breaker can only take a continuous load of 12 amps, 16 amps for a 20 amp breaker.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Oct 2011
    Chicagoland Area
    A display cooler may also have issues with lighting and door heaters
    Oct 2012
    Wisconsin
    Any chance there is somthing else on the same circuit? If you have somthing else pulling amps, and the compressor goes to start it could make it trip.
    I also agree with the others. The compressor could have a hard time starting once in a while. Especially if it shuts off and tries to come back on again without time to equalize. If so equipped, does the plug and receptacle look ok? Plug could be coming loose in outlet and making compressor rapidly short cycle.
    Chicago, IL
    check the flexible wires going to the doors.
    check that none of the wiring for the fans or controls is melted to the defrost heaters.
    I have seen weak start capacitors cause random tripping.
    Dec 2009
    B.C.
    I think I figured it out. After burning my arm on the liquid line, yeah the liquid line, I figured that there could be non-condensables in the condenser. I pulled the charge, brazed in an access on the high side and put in some fresh R-134A. The amps dropped from 12.5 down to 10.6. I haven't heard back from the customer......yet. Thanks for the suggestions guys!
    Pittsburgh
    mullion heaters ?
    Salisbury, Maryland
    Yeah, intermittent problems suck but its most likely tripping for a reason. Had any problems since you pulled charge? Either way I would do like the others said and check your starting components...check run and start cap and make sure the start cap isn't staying in the circuit for too long due to the relay sticking closed. Check the inrush current on the compressor when it starts too. Any history on what was done last? Probably not cause no one seems to know anything when you need the information most hahaha
    Jul 2011
    Lehigh Valley, PA
    Was this a closed system with no gauge ports?
    Dec 2009
    B.C.
    The circuit was on a 15 amp breaker, which isn't ideal for this unit. It only had a port on the suction side. Another thing I'd forgot to mention, the compressor's external overload started to trip once it ran for while and got hot. After evacuating the system, it ran a lot cooler.
    Oct 2005
    B.C. Canada
    Quote Originally Posted by Capz View Post
    Yah, doubt non condesables on a factory sealed sys..
    Denver , Co.
    you gotta wonder with all the China crap coming out
    Outlaw guns? only outlaws will have guns