Results 1 to 8 of 8
    Dec 2006
    Soot in heat exchanger
    I recently started having problems with the Intertherm furnace in my five year old manufactured home. The main burner would come on for a short length of time and blow out, along with the pilot. To make a long story short, it was found that the heat exchanger was plugged with soot from overfiring. This had been slowly building up for a long time, and ultimately was the result of the original installer putting in the wrong orfice during a natural gas-to-propane conversion. The technician is recommending replacing the furnace, as he claims the heat exchanger cannot easily be cleaned. Does this make sense?
    If I do decide to replace the furnace, I am considering replacing it with a more efficient condensing furnace. Are these furnaces readily available for manufactured homes?
    IN THE CRAWL SPACE
    Well replacing the furnace is one option or replacing the heat exchanger.Replacing the heat exchanger is a pain it the butt.What happened to to installing contractor?I feel bad for you but I hope the unit is shut down.
    Don't let anyone talk you into having the thing cleaned because the heatexchanger my be cracked.
    Grottoes VA
    You will never get the thing clean and the soot will return.Replace the heat exchanger
    Jul 2000
    Northern Wisconsin
    Intertherm makes a condensing furnce that is approved for installation in manufactured homes. So does Bryant.
    NW burbs of Detroit
    Yeah soot is a definate telltale. Sorry to say it means the end of your furnace
    Dec 2006
    Kansas City, Mo
    soot
    I would not stop at the heat exchanger, I Would also check the flue piping. When a system starts producing soot, it will travel all the way up the flue, depending on how long it's gone unnoticed. good luck
    Oct 2002
    Illinois
    Just because the furnace sooted up does not mean it is done for. Have a reputable hvac contracator check it out befor you replace anything.
    SE Michigan
    What?? you mean your not going to tell him how to fix the issue Harry?
    “Now the freaks are on television, the freaks are in the movies. And it’s no longer the sideshow, it’s the whole show. The colorful circus and the clowns and the elephants, for all intents and purposes, are gone, and we’re dealing only with the freaks.” - Jonathan Winters