    I myself am relatively new in this field 3+ years. I am currently running all the service for my company. My boss always tells me if you can't figure something out and your in a bind to call tech support, those guys know the equipment inside and out and it's helped me out many times. Good luck keep up the hard work

  3. #29
    Join Date
    Mar 2009
    Posts
    69
    Quote Originally Posted by Dowdhvac View Post
    I myself am relatively new in this field 3+ years. I am currently running all the service for my company. My boss always tells me if you can't figure something out and your in a bind to call tech support, those guys know the equipment inside and out and it's helped me out many times. Good luck keep up the hard work
    x2

  4. #30
    Join Date
    Jan 2006
    Location
    Powell River, BC, Canada
    Posts
    763
    First of all I'd like to commend you for your attitude & work ethic. There's far too many people that would just do what their journeyman said and leave it at that. Your willingness to try & figgure out the 'why' and do things the right way will serve you well in this profession. It may seemlike you're swimming upstream right now (and you are!) but eventually it will get easier for you and you'll start looking forward to new challenges. It feels great when you can come in after others have given up and solve the problem. In a small community word gets around quickly that you are the 'go-to guy' and you can charge accordingly.

    I hope you solved the problem by installing the trap. The vast majority of pressure switch issues are from improper drainage or venting. They're usually fairly easy to figure out, but once in a while you get a head scratcher. I had one a few years ago that drove me around the bend. Intermittant pressure switch faults on a new install. Venting and drains were fairly short and simple and we couldn't ever catch it in the act. We finally ended up pulling the secondary HX and discovered a piece of plastic had gotten in the coupling box between the primarys& secondarys during manufacturing and would move around inside intermittently blocking the drain. You just never know!
    Where are you? Are you done yet? I got ONE more call for you.....

  5. #31
    Join Date
    Oct 2011
    Location
    Sask,Canda
    Posts
    77
    Was sent out to replace the Cleveland Control pressure switch that was installed as we did not at the time have the proper Honeywell pressure switch. The original Honeywell switch had a 0.65 "Wc rating. Used a manometer to get the Cleveland as close as possible to that rating. So, when I put the new Honeywell switch on the furnace it does not run. Codes pressure switch just as it did before. Used the manometer to check the pressure and a multimeter to check the switch. It is working as its rated.... But will not run the furnace. Put the Cleveland switch back in and it runs as it should. So the Cleveland was left in place. Can I just ask what would be up with that...

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event