01-28-2013, 08:50 PM #27
Professional Member
- Join Date
- Jan 2004
- Posts
- 161
Just a guess but if you slow the fan down (hope fully you have adjustable sheaves to get your attained 90 degree split) will your building temp come up to temp. If not take something and block the air flow into the unit to get the 90 degree delta on all three and see if the building temp comes up then you know your moving way too much air. And if you try this and the air temp comes up then you will know what the problem is and you can figure if the calucations are incorrect. I am old school and I always try to prove why!
If you find it bad 3 different ways- ~its bad~
-
01-28-2013, 09:02 PM #28
Professional Member
- Join Date
- Oct 2012
- Location
- Torrington CT
- Posts
- 73
but if you take down the CFM going. I think they need that much air going in. If you block the air coming in it would raise temp but you would not have the air you need.
-
01-28-2013, 09:35 PM #29
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 297
So he needs to check air velocity and verify air flow using the equal friction method, or perform an air balance and confirm the delivered air. Although it is very unlikely that he is moving that much air to over come the required temperature rise.
Again this is a completely sealed combustion which requires 100% outside air. Combustion air is normally delivered by an inline fan and draft by a roof ventilator. It's very common that there is a VFD for both combustion air and draft, however the OP has not stated actual configuration.
Draft will normally be set at a slight negative say -0.10" WC as an example and combustion air at 0.00 " WC. This is a basic design for start up but will need to be corrected based on his design criteria.
-
01-28-2013, 09:53 PM #30
Verify design gas pressure. Measure with all units running and check static pressure. The design of the ICE heat exchanger requires some static to scrub the exchanger. What kind of discharge duct is there?
Never kick a lying dog.
-
02-04-2013, 01:05 PM #31
Regular Guest
- Join Date
- Jan 2013
- Posts
- 11
-
02-04-2013, 01:07 PM #32
Regular Guest
- Join Date
- Jan 2013
- Posts
- 11
-
02-04-2013, 03:41 PM #33
Professional Member
- Join Date
- May 2000
- Location
- Salem, WI US
- Posts
- 43
I would Perform a combustion analysis on the units and compare/ review manufacturers specification on readings, there is something causing this reduced temp rise.
Beta
-
02-04-2013, 07:36 PM #34
I remember doing startup on a very similar unit with the tech from ice and he mentioned that these units have a very low temp rise, like 20 to 30 on high fire....mabey the units are opperating correctly and just not being used for the right application. Have you talked to ice about this? Im thinking this might just be a possibility
-
02-05-2013, 12:07 PM #35
Professional Member
- Join Date
- Mar 2007
- Location
- Sterling Heights, MI
- Posts
- 115
My experience with ICE units is similar. We had about a dozen non-Icecon controlled units which worked great, and they are high temp. rise units. The four newer units controlled by Icecon boards are low temp. rise. You should check with ICE to determine if the settings on the Icecon are proper, as they were the only ones who could program the boards and match them to the unit application. I had to purchase an extra board to keep a unit running when I returned the old board to ICE for service which took a long time. They said not be interchange the board with other units too. These type of units worked best in enclosed areas where minimal cold air entered the zone, not as air turnover units in a large factory setting with the big doors opening or where there was a lot of exhaust. The software to communicate with the board would only work if the board was 100% functional. If there was a malfunction, you could not cummunicate with the board to aid in service. If we need any new units, nothing with an Icecon board is coming in again.coolerik
View Profile View Forum Posts Private Message Add as Contact View Forum Threads
Professional Member Join Date:Oct 2005
Location:B.C. Canada
Posts:387I remember doing startup on a very similar unit with the tech from ice and he mentioned that these units have a very low temp rise, like 20 to 30 on high fire....mabey the units are opperating correctly and just not being used for the right application. Have you talked to ice about this? Im thinking this might just be a possibilityBetter Service Through Knowledge...
RSES, The HVACR Training Authority. www.rses.org
-
02-11-2013, 01:05 PM #36
New Guest
- Join Date
- Feb 2013
- Posts
- 2
I dont mean to post incorrectly, but I cant find a way to private message.
You mentioned the software, is it possible to get a copy of that software? Totally unrelated topic as I am taking over a unit with a BMS and need to verify some settings but I cant seem to find the software they talk about in the documentation to be able to do so.
Thanks in advance!
-
02-11-2013, 05:13 PM #37
Professional Member
- Join Date
- Mar 2007
- Location
- Sterling Heights, MI
- Posts
- 115
Look at these google searches:
www.ice-ww.com/HTDM%20Installation%20Manual.pdf see page 27
http://hvac-talk.com/vbb/showthread....etup-questions
Sorry, that software, laptop and special cable was left behind at the location those units were at. Happy not to have any of those HTDMs. Ours all ran stand-alone with an on board thermostat. Can’t see how a BAS can help anything. Some of your problem may be that the BAS control setup was not done for real life conditions, and again these are low temperature rise units that are supposed to run continuously.Better Service Through Knowledge...
RSES, The HVACR Training Authority. www.rses.org
-
02-18-2013, 11:21 AM #38
Professional Member
- Join Date
- Feb 2013
- Location
- Soon I will be in NE
- Posts
- 16
I have never touched an ICE unit - but they seem to be in the same category as an EVAPCO system, where they do custom design for each application. That being the case (along with my usual disdain for mechanical engineers - sorry guys!) I would check the design of the system itself - Board is calling for 100% - 10v dc output - valve is open - but is the valve the right size? Is there excessive pressure drop through the gas train? If you know your airflow - then you can also know the Btu's needed to get the temp rise you need - then cross reference the Manufacturer's specs on the valve to be sure that it will be able to deliver. If you need help double checking the sizing on the gas train - I have a reference that will help with that.
Also check that the gas pressure doesn't drop when the system fires - sometimes the pressures look good until the system starts.
I had an EVAPCO that was delivered with an undersized TXV because Evapco did not account for the pressure drop across the distributor. When the weirdness starts - do not assume anything is right on a custom system.
-
03-25-2013, 03:08 AM #39
Regular Guest
- Join Date
- Mar 2007
- Posts
- 42
What type of program is hooked up to the systeam?