    WSHP issue

    Today I worked on a mcquay water source heat pump that was tripped on high head upon my arrival. Standing pressures were in an acceptable range so I reset the the unit. The unit kicked on immediately and ran fine with normal pressures and amp draws and TD across coil. After running fine for 10 minutes the head pressure spikes to past 350 and trips off on high head. Unit has a cap tube and low SH. The property manager said that the unit has never really worked properly since it was installed. I figured that there was a restriction in the water lines, but when I checked the strainers they were clean. Also acceptable delta T on the water. Could it be a bad reversing valve? Doesn't make sense how everything runs steady for more than 10 minutes and then boom, head pressure is through the roof. Any ideas?

  2. #2
    Join Date
    Dec 2008
    Location
    New York, ny
    Posts
    189
    What was your suction pressure?? What kind of freon we talking about? Where you running in heating or cooling?

    Sent from my SGH-T999 using Tapatalk 2

  3. #3
    Join Date
    Dec 2008
    Location
    New York, ny
    Posts
    189
    And a model number would be good.

    Sent from my SGH-T999 using Tapatalk 2

  4. #4
    Join Date
    Oct 2005
    Location
    Phoenix, Arizona
    Posts
    382
    cool or heat mode? you have any pressure readings?
    RTFM!!!

  5. #5
    60psig suction and 250psig head while running in cooling mode. This particular unit is never used for heating. I do not have a model number. R22

  6. #6
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,069
    "Acceptable delta T on the water" is kinda vague. What are entering and leaving water temps? Both immediately after startup and when unit trips.

  7. #7
    Join Date
    Aug 2012
    Posts
    2,663
    sounds like --- restriction, but I am preaching to the chior.
    My name is TooCoolforschool and I am a chronic over charger.

  8. #8
    Water in is 68 and water out is 81

  9. #9
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,193
    Even if they don't use it in heat mode, what happens if you run it in such. Sames as in cool and spikes? Might be worth trying.

  10. #10
    Join Date
    Dec 2008
    Location
    New York, ny
    Posts
    189
    Maybe your water reg valve acting up??? Also double check your temp across filter dryer.

    Sent from my SGH-T999 using Tapatalk 2

  11. #11
    Join Date
    Oct 2005
    Location
    Phoenix, Arizona
    Posts
    382
    Yeah I agree with grkmano. If u have a control valve for your condenser water it might be closing on you. Also need to check your circuit setter if u have one to make sure it's not restricting your water flow. You might have a liquid line restriction somewhere. Good
    Luck buddy.
    RTFM!!!

  12. #12
    Join Date
    Mar 2008
    Location
    NC
    Posts
    1,461
    Is this the type that uses a thermistor to control the expansion valve?

  13. #13
    Join Date
    Dec 2008
    Location
    New York, ny
    Posts
    189
    Quote Originally Posted by ncboston View Post
    Is this the type that uses a thermistor to control the expansion valve?
    He said it was a cap tube system... so has to do either filter dryer or water reg.

    Sent from my SGH-T999 using Tapatalk 2

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event