    I recently had a gas valve that was leaking through to the point of being able to smell it as you walk up to the furnace. This got me thinking that I should start checking for them on a clean and check using a leak detector. My question is at what point do you recommend replacing the gas valve? I checked one today(at the orifices) and my detector went off. I turned the gas cock off and waited 30minutes or so and checked again and it still went off. Not sure if I'm getting false positives or its residual. Anyone have any tips? I don't want to rip anyone off ya know

  2. #2
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,551
    Sounds like false readings, soap bubbles don't lie.

  3. #3
    hey if its leaking you replace it. You are not ripping him or her off, you are probably saving their lives. Also try using soap bubbles or some of that leak detection fluid in case your detector is malfunctioning. If there is a leak around those orifices you will see it.

  4. #4
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    4,269
    easy way to check is with a combustion analyzer on shutdown.

    ive also had the pilot valve leaking while no call for heat active. this was a spark ignition setup.

  5. #5
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,367
    Gas valve is allowed to leak 200CCM(0.007062933 CF) an hour as I recall.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,385
    Quote Originally Posted by chevster01 View Post
    hey if its leaking you replace it. You are not ripping him or her off, you are probably saving their lives. Also try using soap bubbles or some of that leak detection fluid in case your detector is malfunctioning. If there is a leak around those orifices you will see it.
    Soap bublles are something you can show the customer also.

  7. #7
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    6,237
    ANSI stds allow trace gas leakage through the seals of the valve into the room at 200cc/hr and 235 cc/hr through the main operator to the burners both at 3/4 psi.

  8. #8
    Join Date
    Jul 2012
    Location
    Cincinnati ohio
    Posts
    252
    Quote Originally Posted by beenthere View Post
    Gas valve is allowed to leak 200CCM(0.007062933 CF) an hour as I recall.
    So how do you measure this? I was told by one of our senior techs that you are supposed to put a manometer on and block the orifices. if it goes to .5"h2o in 5minutes then recommend a new valve and if it makes it to 1" in ten minutes then it needs to be turned off and red tagged. Any thoughts on this?

  9. #9
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,367
    The size of the manifold would also play a large roll in how long it takes to build up to X pressure.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #10
    Join Date
    May 2007
    Location
    Central NJ Area
    Posts
    855
    While operating the system with a combustion analyzer close the gas valve. Watch the CO reading. If it rises after the gas valves is closed then the valve is leaking. I mean if it goes up a few ppm then i wouldn't be worried, but if it spikes up a good amount its time to replace the gas valve.

    Any type of CO or gas/oil issues i always recommend repairing the issue to prevent any bad happens and you are sued. Same goes with any type of saftey limit, delayed ignition or vent piping issues.

    You have to be crazy not to especially wiht people looking for a reason to sue. If customer refuses repair i make sure i have potential injury and death that could happen and make them sign that they understand the issues.

  11. #11
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,740
    you will always detect at the orfice ,check it with bubbles
    We really need change now

  12. #12
    Join Date
    Apr 2012
    Location
    Cleveland
    Posts
    611
    Quote Originally Posted by Nytefog View Post
    While operating the system with a combustion analyzer close the gas valve. Watch the CO reading. If it rises after the gas valves is closed then the valve is leaking. I mean if it goes up a few ppm then i wouldn't be worried, but if it spikes up a good amount its time to replace the gas valve.

    Any type of CO or gas/oil issues i always recommend repairing the issue to prevent any bad happens and you are sued. Same goes with any type of saftey limit, delayed ignition or vent piping issues.

    You have to be crazy not to especially wiht people looking for a reason to sue. If customer refuses repair i make sure i have potential injury and death that could happen and make them sign that they understand the issues.
    Can you explain this a little more please? Do you shut it off at the gas cock, or the gas valve itself? Are you watching co, or co air free? And why would gas leaking cause co to rise?

  13. #13
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    6,237
    Quote Originally Posted by 2141 View Post
    So how do you measure this? I was told by one of our senior techs that you are supposed to put a manometer on and block the orifices. if it goes to .5"h2o in 5minutes then recommend a new valve and if it makes it to 1" in ten minutes then it needs to be turned off and red tagged. Any thoughts on this?

    Well, it's done in the lab with a bubble-o-meter attached to the valve discharge for through the main operator and before the valve with the gas turned off for leakage through the valve seals. http://www.bubble-o-meter.com/index.php

    Correct info. on using CA and valve failing to close to a point. You can also use a gas sniffer or manometer at the gas valve outlet and kill the power then see if you still detect gas. Bubble meter is lab certified accuracy and quantitative. Careful with soap bubble solutions: must be non-corrosive and never painted over the vent on a gas regulator. Use sniffer. If steady leak at vent, indicates blown diaphragm, possibly from overpressure.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event