    I've seen charge compensators in JCI products (York, Luxaire, Coleman and JCI), Rheem brands, Goodman/Amana brands etc.

    All they are is a cannister with the suction/hot gas discharge line running through it and a branch off of the liquid line feeding the shell of the canister. In cooling mode, the large line running through the charge compensator gets cold and condenses the refrigerant fed by the liquid line so that the cannister fills up with liquid refrigerant, taking that much refrigerant out or the system. In heat mode, the large line going through the charge compensator is hot, boiling off liquid refrigerant in the compensator and forcing it into the system.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  2. #41
    Join Date
    Dec 2011
    Location
    North Texas
    Posts
    647
    I know what you are talking about now RoBoTeq, you've pretty much described what me and everybody else I've worked with and went to school with calls an accumulator. In fact the the description you gave reads almost like the description for an accumulator for a heat pump out of my old textbook. It never called it a charge compensator.

  3. #42
    Join Date
    Jul 2005
    Posts
    5,153
    Quote Originally Posted by clifpaul View Post
    I know what you are talking about now RoBoTeq, you've pretty much described what me and everybody else I've worked with and went to school with calls an accumulator. In fact the the description you gave reads almost like the description for an accumulator for a heat pump out of my old textbook. It never called it a charge compensator.
    Not even close. Completely different device.

  4. #43
    Join Date
    Dec 2011
    Location
    North Texas
    Posts
    647
    Guess I got myself mixed up.But at least I learned something...
    charge accumulator [ATTACH=CONFIG]357621[/ATTACH

    suction accumulator] Name:  images.jpg
Views: 116
Size:  4.7 KB

    I stand corrected gentlemen
    Attached Images Attached Images  

  5. #44
    Join Date
    Dec 2011
    Location
    North Texas
    Posts
    647
    My apoligies for the lousy picture posting btw.

  6. #45
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,852
    Quote Originally Posted by clifpaul View Post
    My apoligies for the lousy picture posting btw.
    That's a better pic than anything I've found so far.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  7. #46
    Join Date
    Dec 2011
    Location
    North Texas
    Posts
    647
    Thanks. I learned something myself since I didn't know there was a difference.

  8. #47
    Join Date
    Mar 2002
    Location
    Eufaula OK
    Posts
    4,175
    Name:  CompensatorSS.bmp
Views: 142
Size:  337.4 KB

    Here is a pretty good pic showing the difference between a compensator and an accumulator.


    Don't know why pic did not show but here is the link. http://www.cwis.net/~mallie/CompensatorSS.bmp
    Last edited by Jax; 02-17-2013 at 12:42 PM. Reason: pic no show

  9. #48
    Join Date
    Sep 2012
    Location
    Missouri
    Posts
    47
    Good conversation guys. Learned a couple things.

  10. #49
    Join Date
    Jul 2007
    Location
    Delaware
    Posts
    3,823
    Last used in the 90's. Back when Robo had big hair and tall shoes!

  11. #50
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,852
    Quote Originally Posted by energy star View Post
    Last used in the 90's. Back when Robo had big hair and tall shoes!
    LOL! What makes you think RoBo doesn't still have big hair? Well, maybe not as big, but it still covers all of my head. And the only tall shoes I ever wore were boots.

    As for charge compensators, they are still out there.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  12. #51
    Join Date
    Nov 2007
    Location
    Sherman, TX
    Posts
    9,441
    Quote Originally Posted by SBKold View Post
    Don't forget its still just a refrigeration system.
    Exactly !!

    It makes my skin crawl, when someone claims that you can't "properly" charge a heat pump system in the winter....

    If you can't charge a heat pump in the winter, how do you charge a wine display in a liquor store at any point in the year?

    That's the difference between guys with "knowledge" and guys with "understanding"...
    Technical incompetence is NOT a sales tool....

  13. #52
    Join Date
    Nov 2007
    Location
    Sherman, TX
    Posts
    9,441
    Quote Originally Posted by clifpaul View Post
    X@. I've seen accumulators, but I've never seen or heard of a charge compensator til now.
    Paul, next time you look at an old Rheem heat pump indoor coil, you might notice a "chunk of copper" about 1-3/8 inches in diameter along the side of the coil. That is one type of compensator. Newer units have them in the outside unit. Often on Rheems, they are blue in color.
    Technical incompetence is NOT a sales tool....

Page 4 of 5 FirstFirst 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event