01-23-2013, 11:31 PM #14
-
01-24-2013, 12:39 AM #15
-
01-24-2013, 10:31 PM #16
Sorry for the miss-understanding. What I was trying to get across was simply that it is better to charge in the cooling mode at manufacture specified OAT. However, we don't live in that magical world. Yes it is best to weigh charge in ( keeping mindful of line length). If weight info is nowhere to be found or line length is not able to be determined for example lines behind walls and or condenser is 3 doors down and on the other side of the street because that's were the architect decided it looked good there, SC and SH can be used. The miss understanding in the difference in refrigerant amount between heating and cooling was not explained well my bad. What I meant was when you do charge in cold conditions in the heating mode you may find when in warm conditional and the unit is switched to cool you may find the unit to be a few ounces low. This is do to the slight loss of capacity in the heating mode and conditions compared to the cooling mode and conditions. The accumulator is there to protect the compressor in the cool/ cold condition to prevent slugging the compressor. I guess the point I was trying to get across was it is not a bad practice to make a visit in the spring or early summer just to verify the charge is correct, to ensure the customer is getting the full performance from there system. Sorry for the miss understanding.
-
01-25-2013, 01:27 AM #17
And yes I do agree that the difference in the size of indoor and out door coils does have a contributing factor as well. Maybe not as much in an air to air heat pump but the logic can be somewhat corilated to a Direct Exchange Geo. I know it's a totally different beast but none the less the basic principle is there.
-
01-25-2013, 06:24 AM #18
Professional Member
- Join Date
- Feb 2012
- Location
- Durham, NC
- Posts
- 64
Riddle me this:
Why is it that one can charge a heat pump in cool mode, it runs fine all summer. Then come winter time, the system performs poorly, produces symptoms of overcharge, then performs just fine once some refrigerant is reclaimed?
What I'm trying to say is that its easy to overcharge a heat pump in cool mode, because it will use more refrigerant in cool mode.
And NO, we don't go out in the fall, pump some refrigerant out and return in the spring to put it back in. However, a heat pump is critically charged, slightly overcharged it will perform poorly in heat mode, slightly undercharged it will perform poorly in cool mode.
Bottom line, a charge that is considered "undercharged" in cool mode will perform fine in heat mode. Why? Because the system doesn't need the extra refrigerant that it needs in cool mode.
The end.
-
01-25-2013, 08:06 AM #19
I actually think we are all saying very similarly the same thing, only in a bit different way. While we can pretty much make any indoor coil work for a cooling only application by metering and charging to that particular coil and metering device, when we start changing up the indoor coil function and the outdoor function, the two coils either need to be close in physical capacity or some sort of charge compensator, collector of refrigerant if you will, to keep the refrigerant charge controllable in both heat and cooling modes.
Government is a disease......masquerading as its own cureEcclesiastes 10:2 NIV
-
01-26-2013, 07:52 PM #20AGREED....I actually think we are all saying very similarly the same thing, only in a bit different way.
................myself, i charge all units by SH and SC no matter the conditions
-
01-30-2013, 06:05 PM #21
Regular Guest
- Join Date
- Jan 2013
- Posts
- 6
All of the methods of charging in the winter will get you close. But there isn't any way you can be absolute without know the exact specs. And weighing it in. The accumulator is designed for keeping liquid from getting to the compressor but its because one mode requires more refrigerant than the other. It's simply because while running in the heat pump mode as the ambient temp. Drops and/or frost begins to form on the coil flooding will occur
-
01-30-2013, 07:33 PM #22
Regular Guest
- Join Date
- Jan 2013
- Posts
- 6
I meant its not bra cause o e mode requires more refrigerant than the other. My bad
-
01-30-2013, 07:34 PM #23
Regular Guest
- Join Date
- Jan 2013
- Posts
- 6
I give up I can't type today. My bad guys
-
02-01-2013, 08:34 AM #24
Professional Member*
- Join Date
- Oct 2002
- Posts
- 674
Many units, now, have no suction accumulators. They are reliant on a carefully matched balance of theinside and outside coils. Charge is very critical.
-
02-02-2013, 09:59 AM #25
Professional Member
- Join Date
- Nov 2011
- Location
- Philadelphia, PA
- Posts
- 143
-
02-02-2013, 10:03 AM #26
Professional Member
- Join Date
- Nov 2011
- Location
- Philadelphia, PA
- Posts
- 143
I was told by a goodman rep you cannot charge a unit accurately in heat mode.