Results 66 to 73 of 73
-
01-26-2013, 11:38 AM #66
Professional Member*
- Join Date
- May 2004
- Location
- south louisiana
- Posts
- 2,196
Chad,
before you write us all off...
try what teddy bear suggests:
Operate you fan "on" mode for a couple days to test "the condensation in the ducts" theroy.
personally...I'm not sure about that, but would be interested in what you find out. as teddy bear
says..its a learning experience.
better to resolve what is happening than to live with it...right?
investing a week of your time may provide a solution to your RH issues.
living in the south...I've seen the issues caused by the whole chinese drywall fiasco.
corrosion of copper in electrical, hvac causing homes to be re-wired, hvac system completly
changed out...breathing issues. its nothing to make light of.
keeping the thread on track is always difficult. so just ignore what doesn't apply & use
could help you. insulting homeowners is not the intent of this forum.
best of luckThe cure of the part should not be attempted without the cure of the whole. ~Plato
-
01-26-2013, 11:51 AM #67Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
01-26-2013, 12:47 PM #68
Regular Guest
- Join Date
- Mar 2012
- Posts
- 35
-
01-26-2013, 01:37 PM #69
Circulate. You may want to keep the dehumidifier running until that ductboard dries out.
An answer without a question is meaningless.
Information without understanding is useless.
You can lead a horse to water............
http://www.mohomeenergyaudits.com
-
01-26-2013, 02:52 PM #70
Professional Member*
- Join Date
- May 2004
- Location
- south louisiana
- Posts
- 2,196
a building science article that in part addresses what is going on is Chad's house.
only part of the article...see picture #4
http://www.buildingscience.com/docum...rces/retrofits
Photograph 4: Window Condensation - Interior moisture levels go up due to reduced air change and relative humidity adjacent cold window surfaces rises sufficiently to condense water. How to fix this problem? Lower the moisture content of the interior air with dilution ventilation or warm up the surface of the windows by replacing the windows with better windows or do both.
So Far:
1-reduced Rh by adding dehumidifier
2-are the kitchen vent fan & bath fans vented out of the attic?
3-leaving fan set in on position..in case there is condensation in the duct work. as per Teddy Bear's postings.
4-windows...see my first post about metal frames of windows & condensation.
also...while letting the blower run in winter to resolve the issue of moisture in ductwork that is potentially ongoing,
the side note to that is fan setting in the summer.
for cooling season when a/c use is constant, you set the fan to auto.
reason for that is...RH removed by a/c will collect on coil, when fan is set
to on position...it releases this moisture back into the house when compressor cycle ends.
when fan shuts down as unit shuts down, the moisture then is released to the pan
and drains away.
so...are your kitchen & bath fans vented out of the attic??
best of luck.The cure of the part should not be attempted without the cure of the whole. ~Plato
-
01-26-2013, 03:44 PM #71
Regular Guest
- Join Date
- Mar 2012
- Posts
- 35
The kitchen is not. I'm not sure about the three bathroom exhaust fans. Looking in the attic above where one of the fans are located, there is a vent pipe that exits the roof, but this might just be for plumbing. Could the exhaust fans be tied to that. I know I'm not very much help on this. Shame on me for not knowing more about my own home. At the very moment, I am running the fan in the "on" position with my stand alone dehumidifier running full blast.
-
01-26-2013, 04:26 PM #72
Professional Member*
- Join Date
- May 2004
- Location
- south louisiana
- Posts
- 2,196
I never vent bath fans thru the roof. they just don't have enough 'push' to go up and out.
instead I vent into soffits. you can tell which joist bay has venting because you'll see light from
outside.
you'd have to first...find the bath vent fan, if its covered with cellulose, turning it
on will help you to locate it. if it has a backdraft damper..or not...it will blow the cellulose
around..helping you to find it.
backdraft damper needs to be installed so that when fan is off, the damper closes.
suprising the number of bath fans that the bd damper is installed incorrectly.
usually bd dampers are the same size as dryer vents. I use a foil flex dryer vent
attached to bd damper. lenght of venting will easily reach into soffit, cutting off
excess vent. you want to keep the vent run as straight as possible.
I use mastic tape to attach venting to damper, then damper to bath vent fan.
code also says that bath fans are to be vented out of soffits. but to go
from venting into attic to venting into soffit suffices for existing homes.
bath fans & stove fans that vent into the attic introduce a lot of humidity into attic.
when bath fans vent directly into insulation they can over time cause mold growth.
stove vents vented into the attic put grease particles in the attic.
a fireman once told me that the cause of a lot of attic fires was from
stove vents terminating in the attic and not being vented outside of attic.
codes dictate this, but in existing homes...we get away with a lot more than new construction.
at this very moment...I'm consitering turning the a/c on. 75 degrees with 70% RH outside today!The cure of the part should not be attempted without the cure of the whole. ~Plato
-
01-26-2013, 05:54 PM #73
One may get away with "cutting corners" by trying to vent bathroom exhaust out of the attic soffits in hot climates, but it should NEVER be done in the colder climates. This is especially true if you have your attic air sealed and improve the insulation levels. What happens is that the air sealing & improved insulation makes your attic colder - because it is no longer being warmed by your homes conditioned air leaking into the attic- and all of that warm moist air that you think you are "venting" through the soffit is simply being drawn back into the attic, where is condenses on the cold roof. As seen in this video, it can lead to some serious problems.
An answer without a question is meaningless.
Information without understanding is useless.
You can lead a horse to water............
http://www.mohomeenergyaudits.com


Reply With Quote