    A LOT of condensation on widows and sills

    Hello all! I live in south Alabama and the past few nights the temp. has gotten around 35-39 degrees. I have a brand new Trane 16 seer variable speed heat pump with a thermostat that has humidity control. I keep my set temp. at 70 degrees when i go to bed. The next morning, I have pools of water on my window sills and the windows have droplets of water all over them and are also fogged over. I have also noticed when the heat is running, it is putting my humidity level between 64 and 70. To me that doesn't sound normal. Does the high humidity level have something to do with this? Also, the house is a new home with upgraded insulation. The windows are double paned, but are metal, not vinyl, which I don't think the winows have anything to do with what's going on. I guess the humidity control doesn't work unless the a/c is running, correct? What the heck is going on? I'm really getting frustrated. Thanks for any help that can be offered.

    Chad

  2. #2
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,927
    Post Likes
    New homes tend to have high humidity due to the new materials,i.e., lumber and plaster or drywall. Your level of humidity is way too high. New homes are built to much tighter standards, installing a fresh air intake might work for you. I know that HVAC in the south must be an entirely different animal because of the high outdoor humidity.

  3. #3
    Join Date
    Jul 2012
    Location
    New England
    Posts
    9
    Post Likes
    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 01-20-2013 at 10:30 AM. Reason: Non AOP member

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    jazpek

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.



  5. #5
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,790
    Post Likes
    window choice has everything to do with it.

    metal is an excellent conductor of heat/cold.
    the window frames contribute to the condensation.
    look at the window numbers..solar heat gain coefficients
    and u-factors.

    a double paned vinly with low e coating will have a .37 shgc & u-factor.
    take that same insulated glass unit and put it into a metal frame
    and these numbers jump to .57 shgc & ufactor.

    as it gets cold outside, these temps transfer thru the metal.
    even thermal break doesn't stop the transfer.
    so when the cold of the outer frame reaches the warm of
    the inner frame..they condensate.

    granted new construction materials may contain higher moisture
    content. this usually settles down to normal range in a full
    heating cooling season.

    adding supplimental dehumidification helps, but this is really
    a poor window choice that has been made.
    in the summer time condensation will be to exterior of
    windows.

    if hvac system is oversized, then in summer it will not run
    long enough to dehumidify.
    ideally 50% RH inside the home is what we try to achieve
    in the south.

    you may want to look into stand alone dehumidifiers.
    if this works well then investing in a whole house
    dehumdificiation sytem is a good choice.

    best of luck.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  6. #6
    Join Date
    Mar 2012
    Posts
    56
    Post Likes
    Thread Starter
    George2

    What exactly is a fresh air intake? Also, what size dehumidifier would I need?(not the whole house type, just one you sit on the floor) The living area of the the home is 2200sf.

    Thanks

    Chad

  7. #7
    Join Date
    Aug 2010
    Location
    West Monroe, LA
    Posts
    1,594
    Post Likes
    Quote Originally Posted by energy_rater_La View Post
    window choice has everything to do with it.

    metal is an excellent conductor of heat/cold.
    the window frames contribute to the condensation.
    look at the window numbers..solar heat gain coefficients
    and u-factors.

    a double paned vinly with low e coating will have a .37 shgc & u-factor.
    take that same insulated glass unit and put it into a metal frame
    and these numbers jump to .57 shgc & ufactor.

    as it gets cold outside, these temps transfer thru the metal.
    even thermal break doesn't stop the transfer.
    so when the cold of the outer frame reaches the warm of
    the inner frame..they condensate.

    granted new construction materials may contain higher moisture
    content. this usually settles down to normal range in a full
    heating cooling season.

    adding supplimental dehumidification helps, but this is really
    a poor window choice that has been made.
    in the summer time condensation will be to exterior of
    windows.

    if hvac system is oversized, then in summer it will not run
    long enough to dehumidify.
    ideally 50% RH inside the home is what we try to achieve
    in the south.

    you may want to look into stand alone dehumidifiers.
    if this works well then investing in a whole house
    dehumdificiation sytem is a good choice.

    best of luck.
    This is a very good post. energyraterla is correct. The best double pane window with low e and thermal break still not hold a candle to good double pane vinyl window.

    Over the years all the improvements to metal windows have really been non successful as one thing remains the metal frame which will conduct heat and cool. Think about it put a piece of metal and vinyl in the sun and wait just a few minutes which one gets hotter? The metal does plan and simple. While the low e and thermal break just address the glass not the metal frame.

    It still amazes me that this day in time that buliders are still using metal windows? In the past when homes were not as tight people would not see the problems that you are due to the home having leakage. Over the past 20 years all the thought process of building a new home has gone to getting the House tigher and they have become so right in some cases that fresh air make up most be part of the heating and cooling systems so the home can breath.

    Freash air makeup is when you introduce outside air into the home to allow it have healthy air changes per hour. While the humdity levels you are reporting are very high and need to looked at before any more damage is done to window sills, inside of the home etc... Depending on your home and how you run your system you would want in the winter for your home to be somewhere between 30-40% on average and during the summer 45-55% humdity levels. A good dehumditfer might be the answer to remove all the excess moisture in your home.

    You say you have a Trane 16 seer heat pump. What are the model numbers of the system and how much aux. heat due you have? If the system is oversized during the summer your system will not run long enough to remove the humdity in the home and during the winter usually heat dries out the home but it is not designed to remove humidity like the a/c does. Dehumditfer again might be you best option to help with this. What does your builder and hvac installer have to say about the problem?

    More then lickly in your home it is just really tight and the metal is conducting the opposite temp on the windows vs the indoor with the metal windows. I understand that this is not what you want to hear in a new home but this are things that you need to address before they get worse and while your home is still under warranty. Please keep us posted on the outcome!

  8. #8
    Join Date
    Mar 2012
    Posts
    56
    Post Likes
    Thread Starter
    Quote Originally Posted by duckman06 View Post
    This is a very good post. energyraterla is correct. The best double pane window with low e and thermal break still not hold a candle to good double pane vinyl window.

    Over the years all the improvements to metal windows have really been non successful as one thing remains the metal frame which will conduct heat and cool. Think about it put a piece of metal and vinyl in the sun and wait just a few minutes which one gets hotter? The metal does plan and simple. While the low e and thermal break just address the glass not the metal frame.

    It still amazes me that this day in time that buliders are still using metal windows? In the past when homes were not as tight people would not see the problems that you are due to the home having leakage. Over the past 20 years all the thought process of building a new home has gone to getting the House tigher and they have become so right in some cases that fresh air make up most be part of the heating and cooling systems so the home can breath.

    Freash air makeup is when you introduce outside air into the home to allow it have healthy air changes per hour. While the humdity levels you are reporting are very high and need to looked at before any more damage is done to window sills, inside of the home etc... Depending on your home and how you run your system you would want in the winter for your home to be somewhere between 30-40% on average and during the summer 45-55% humdity levels. A good dehumditfer might be the answer to remove all the excess moisture in your home.

    You say you have a Trane 16 seer heat pump. What are the model numbers of the system and how much aux. heat due you have? If the system is oversized during the summer your system will not run long enough to remove the humdity in the home and during the winter usually heat dries out the home but it is not designed to remove humidity like the a/c does. Dehumditfer again might be you best option to help with this. What does your builder and hvac installer have to say about the problem?

    More then lickly in your home it is just really tight and the metal is conducting the opposite temp on the windows vs the indoor with the metal windows. I understand that this is not what you want to hear in a new home but this are things that you need to address before they get worse and while your home is still under warranty. Please keep us posted on the outcome!
    Which dehumidifier would you suggest that will not break the bank?

  9. #9
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,790
    Post Likes
    start with a stand alone dehumidifier.
    if it works well, then upgrade to whole house dehumidifier.

    I have a 15 SEER heat pump. air handler is variable speed.
    this alone keeps RH in 55% range, in the summer.
    for additional dehumidification I have Ultra aire 70H
    this brings RH down to 45% in summer. and it is very
    comfortable.

    have you had a blower door test (& duct test) on your
    home, or is the assumption that the house is tight due
    to newness of build?

    you should talk to Teddy Bear about whole house dehumidifiers.
    he really knows his stuff.

    ty duckman.

    best of luck.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  10. #10
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    As general rule, reducing indoor %RH when the outdoor dew points are <55^F is most efficient done by increasing fresh air change. Do you have any fresh air ventilation? High indoor %RH during cool weather indicates a lack of fresh air change. Resulting in a buildup of moisture from the occupants and activities. Is there a crawlspace with uncovered earth or other sources of moisture?
    Anyway, operate the bath fans 24/7 until humidity falls.
    All occupied homes need a fresh air change in 4-5 hours when occupied. This is an important part of indoor air quality. During cold weather, the indoor dew point must be kept low enough to avoid condensation on any indoor surface. During the summer months allong with the fresh air change, keep the indoor moisture below 50%RH for comfort and to avoid mold and dust mites.
    In your climate, a whole house ventilating dehumidifier is the most practical device to do all of this. Check out the Ultra-Aire 70H as minimal piece of equipment to do this. Check my past post for more info.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  11. #11
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,790
    Post Likes
    ahhh....there you are!
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  12. #12
    Join Date
    Mar 2012
    Posts
    56
    Post Likes
    Thread Starter
    Quote Originally Posted by teddy bear View Post
    As general rule, reducing indoor %RH when the outdoor dew points are <55^F is most efficient done by increasing fresh air change. Do you have any fresh air ventilation? High indoor %RH during cool weather indicates a lack of fresh air change. Resulting in a buildup of moisture from the occupants and activities. Is there a crawlspace with uncovered earth or other sources of moisture?
    Anyway, operate the bath fans 24/7 until humidity falls.
    All occupied homes need a fresh air change in 4-5 hours when occupied. This is an important part of indoor air quality. During cold weather, the indoor dew point must be kept low enough to avoid condensation on any indoor surface. During the summer months allong with the fresh air change, keep the indoor moisture below 50%RH for comfort and to avoid mold and dust mites.
    In your climate, a whole house ventilating dehumidifier is the most practical device to do all of this. Check out the Ultra-Aire 70H as minimal piece of equipment to do this. Check my past post for more info.
    Regards TB
    Thanks for all the replies. As for the first question, I do not have any fresh air ventilation system. As for the second question, I am built on a slab, so no crawlspace or basement. Also, as I stated in my original post, it seems that when the heater kicks on, the humidity in the house shoots up all of a sudden. I just don't understand this. How much does the ultra-aire 70h cost and how much would it cost to have it installed? Thanks again, everyone.

    Chad

  13. #13
    Join Date
    Oct 2006
    Location
    So. NH
    Posts
    824
    Post Likes
    Quote Originally Posted by clllclal View Post
    Thanks for all the replies. As for the first question, I do not have any fresh air ventilation system. As for the second question, I am built on a slab, so no crawlspace or basement. Also, as I stated in my original post, it seems that when the heater kicks on, the humidity in the house shoots up all of a sudden. I just don't understand this. How much does the ultra-aire 70h cost and how much would it cost to have it installed? Thanks again, everyone.

    Chad
    Is there a humidifier installed in your system? I'm not that familiar with your climate but it seems to me that 70% is just too high to happen on it's own. I'm wondering if there is one it may not be properly wired or set and is running all the time. If not are there any other large sources of humidity like a hot tub?

  14. #14
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,927
    Post Likes
    [QUOTE=clllclal;15033881]George2

    What exactly is a fresh air intake? Also, what size dehumidifier would I need?(not the whole house type, just one you sit on the floor) The living area of the the home is 2200sf.

    Thanks

    The cheapest and easiest way (for fresh air) is to run a 6" or 7" pipe from the outside directly into the return air duct. I live in the midwest and I assume that your humidity varies greatly from ours but I had a customer that had tightened his home and developed excess humidity. I mean it was dripping like I had never seen.

    I told him to try the "simple" fresh air method and I have to say it worked like a charm. Every time he sees me he can not stop talking about the difference that it has made. He's a customer for life!

  15. #15
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,790
    Post Likes
    no pricing here OP.

    stvc...high humidity does just happen. right now it is 55 degrees and 59% Rh outside.
    inside temp is 65 degrees % Rh is 64%.
    no heat for the past few days...its been nice outside.
    turned off heat & april aire system.

    OP..don't add a fresh air intake to the return unless you need it, otherwise you
    are introducing more RH into the house. the most I've ever added was a 4"
    duct with a barometric damper to open only when the house enters a negative
    pressure. introducing the air that a 6 or 7" duct will move...is a lot. esp if it is open
    all the time.

    try the stand alone for a while. run it year round. see what results you get.
    then invest in whole house system.

    check your return air, r/a leaks contribute to high indoor Rh.

    best of luck
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  16. #16
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,974
    Post Likes
    What kind of water heater do you have? Natural draft?
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  17. #17
    Join Date
    Oct 2006
    Location
    So. NH
    Posts
    824
    Post Likes
    Quote Originally Posted by clllclal View Post
    Thanks for all the replies. As for the first question, I do not have any fresh air ventilation system. As for the second question, I am built on a slab, so no crawlspace or basement. Also, as I stated in my original post, it seems that when the heater kicks on, the humidity in the house shoots up all of a sudden. I just don't understand this. How much does the ultra-aire 70h cost and how much would it cost to have it installed? Thanks again, everyone.

    Chad
    From what inside/outside temp and humidity are you raising the inside temp when the heat turns on? A sudden surge is not normal in my heating climate.

  18. #18
    Join Date
    Mar 2012
    Posts
    56
    Post Likes
    Thread Starter
    As I stated in my OP, for some reason the humidity in my house just seemed way too high. We always turn on the exhaust fans when showering and also while cooking. With the time of year it is the A/C is not running, so no dehumidifying effect. I went to my local Lowe's yesterday and purchased a 50 pint dehumidifier. After only running it for a few hours, the humidity level on my Trane tstat was down to about 47%. It was pretty chilly last night and I had the heat set at 69 degrees and when I woke this morning, no fogged windows and they were also dry. I have dumped a couple of full buckets of water out of that thing. If it is just as simple as running the dehumidifier for a few hours during the day, I'll take that. Otherwise, I just wish I knew why the humidity level in my house is so high. I know I said it was new construction, but it has already been a little over a year. Thanks everyone for your input in this matter.

    Chad

  19. #19
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,974
    Post Likes
    What kind of water heater do you have? One with a metal flue and a draft diverter?
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  20. #20
    Join Date
    Mar 2012
    Posts
    56
    Post Likes
    Thread Starter
    Quote Originally Posted by tipsrfine View Post
    What kind of water heater do you have? One with a metal flue and a draft diverter?
    Actually, I have 2 hot water heaters. Both of them are in the attic.

Page 1 of 4 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •