chasing duct work blockage
I work in a hospital, a few days ago we had a interesting coincidence we had to test a fire door later in the day we had a comlaint of no cooling in some areas. we found we were not getting air past a certian area so we started looking at smoke and fire dampers and fornd the a airline blown off a air actuator. Now my question is there a better way look for a blockage or do you do the same thing we had to do just start moving celing tile and chasing the duct work?
-
01-19-2013, 08:48 PM #2
Thread relocated to "Tech to Tech"
-
01-19-2013, 09:14 PM #3
Professional Member
- Join Date
- Jan 2013
- Location
- Central Arkansas
- Posts
- 22
thanks chris I realised afterwords I posted in the wrong place
-
01-20-2013, 06:42 PM #4
Professional Member
- Join Date
- Jan 2013
- Posts
- 19
With Pneumatic there is little you can do but to trace out the lines to find the failure with a BAS system with the appropriate points you can find the location through point failures or duct pressure readings if this is monitored or temp sensor monitors. Also if it is a hybrid system you may be able to use the BAS to pinpoint the point of failure.
-
01-21-2013, 02:59 AM #5
I measure duct static pressure with a manometer every 20 ft or so until a general section is located with a restriction. Then I remove ceiling grids to check for dampers/ actuators in that vicinity.