    Jan 2013
    Central Arkansas
    chasing duct work blockage
    I work in a hospital, a few days ago we had a interesting coincidence we had to test a fire door later in the day we had a comlaint of no cooling in some areas. we found we were not getting air past a certian area so we started looking at smoke and fire dampers and fornd the a airline blown off a air actuator. Now my question is there a better way look for a blockage or do you do the same thing we had to do just start moving celing tile and chasing the duct work?
    Mount Airy, MD
    Thread relocated to "Tech to Tech"
    Jan 2013
    Central Arkansas
    thanks chris I realised afterwords I posted in the wrong place
    Jan 2013
    With Pneumatic there is little you can do but to trace out the lines to find the failure with a BAS system with the appropriate points you can find the location through point failures or duct pressure readings if this is monitored or temp sensor monitors. Also if it is a hybrid system you may be able to use the BAS to pinpoint the point of failure.
    In a van by the river
    I measure duct static pressure with a manometer every 20 ft or so until a general section is located with a restriction. Then I remove ceiling grids to check for dampers/ actuators in that vicinity.
    ## + years in the field never made you a know-it-all This industry is far more diverse than you are