Results 1 to 4 of 4
  1. #1
    Join Date
    Jan 2013
    Posts
    2
    Post Likes

    Central air question

    I’m planning to have central air installed this summer and have a few questions. I have a 15 year old, two story colonial that’s 3,000 square ft. It has a Carrier 58PAV111-16 furnace that’s the same age as the house. The furnace is located at one end of the house and, due to patio & landscaping, I would like the A/C unit located at the other end. The distance between the units would be approximately 70 ft.

    - Can anyone tell me if there is an issue with such a long run between the two units?
    - Am I setting myself up for trouble down the road?
    - Would there be a huge price increase for materials with this design?
    - Will my Carrier furnace support the addition of central air or will I need to replace it?

    Thanks

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    39,011
    Post Likes
    70' should be OK
    No
    No
    Yes, that furnace is fine to add A/C to up to about 3.5 tons. A GOOD dealer would do a load calc to tell you what size your house really needs.

  3. #3
    Join Date
    Jan 2013
    Posts
    2
    Post Likes
    Thread Starter
    Thanks for the information. I read somewhere that a rule of thumb is 1 ton/500 square ft. So, that would put me at 6 tons for my 3000 sq/ft house and based on your post, would be outside the specs for my furnace. Is this correct?

  4. #4
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    1,803
    Post Likes
    Only way to know is have heat gain calls done. I suspect 6 tons to be very large.
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.