    I had my oil furnace tuned and cleaned, they found the breech draft to be -14 and the overfire draft to be -8. Do you think I should have a draft regulator installed? Thank you in advance.
    May 2012
    Upper Michigan
    All oil burners should have a barometric damper
    Jan 2006
    Powell River, BC, Canada
    Quote Originally Posted by Joehvac25 View Post
    Absolutely! The FIRST thing you do when setting up an oil burner is adjust the draft! Every install manual I have seen for oil appliances state that a barometric damper/draft regulator are REQUIRED. About those numbers, did you mean -0.14 and -0.08? Most units want -.01 to -.02" over fire and -.02 to -.04" at the breach, although there are some that operate ant a positive pressure over fire. That large of a difference between over fire and breach draft usually means a partially plugged heat exchanger. Did the tech remove the cleanouts and flue pipe to inspect the inner HX passages? I'm thinking not.
    Where are you? Are you done yet? I got ONE more call for you.....
    SW Wisconsin
    Quote Originally Posted by HCBeav13 View Post
    This is a job for an experienced oil furnace technician; no tinkering by anyone else.
    Way too much draft; Not an efficient situation.
    What temp was the flue gas? ________
    The barometric damper (that it must have) comes shipped with the weight on the right side for vertical flue pipes; if it's a horizontal pipe switch the weight to the left side. [/B]
    I defer to the gasguy post above! Also, I agree, may not have properly cleaned the HX passages.
    Jan 2013
    I believe the measurements were done in pascals (pa) and not inches of water column (inwc), not completely sure about this though. So I believe the conversion would be...
    Breech Draft would be -0.056
    Overfire Draft would be -0.032
    Not sure what you mean by HX passage?
    Sorry I am just starting to learn about my oil furnance (first time as a homeowner)
    Here are some other measurements from the report sheet if that helps...Net Stack 522, CO2 10.9, O2 6.5, Smoke 0, Efficiency 82.2%, CO Reading 39, Fuel Pump 100 psi, Safety timing 45 sec, and water 1/2 in.
    Just to give you an idea about the oil furnace it is a York (1988), forced air w/ Beckett.
    Thanks again for all your help. I am pretty sure I need the barometric damper, I am just looking for some other opinions as well.
    SW Wisconsin
    Well, that changes everything & looks more like it.
    HX, or HT-EX, is short for 'heat exchanger' - passages.
    He may have done a good job cleaning HX passages.
    Without a barometric damper the wind levels & outdoor temperature differentials will affect the draft of the burner too much.
    Keep that service data in a safe place to be used during the next service.
    Altmar, New York, United States
    if you have a poo. pressure boiler, would this still allow it to stay positive? i may try it at my own house as a test. i have many,many biasi b10 boilers out there. not one has a problem. biasi must spec no barro for a reason right? is it because of it not being a neg. system?
    May 2012
    Upper Michigan
    Quote Originally Posted by snupytcb View Post
    I found this and it shows baros, http://www.qhtinc.com/wp/wp-content/...ual-081312.pdf
    It does show to install one if needed because it is a positive pressure boiler. Most cases do not require. Of course I may have just been lucky all these years.lol. But I doubt it, black clouds don't carry good luck. My cloud is hanging tight to me today, I went to bring my dump truck home and it is buried in the mud. And now has a blown break line. Damn this black cloud.lol.
    May 2012
    Upper Michigan
    Lol I didn't really read the manual just looked at the pics, I've never seen one of them boilers so can't say for sure. Sounds like your having a lovely day, if it were here it would be froze in the mud, reminds me of the time I had a Toyota pickup with 38"s and 5:29s, went out to my deer blind through a mud hole and later when I left my drums were frozen solid and stripped half the ring gear off In the rear. That's what 4 low and lockers front and rear does I guess lol.
    Jan 2006
    If you are correct in your units of measure, then that is a lot better. Still a tad on the high side, but not too bad. Might be able to get a bit better efficiency yet. Did they check the temperature rise? The heat exchanger (HX) usually has a couple of removable cleanout ports as well as removing the flue pipe to remove soot buildup from the inside surfaces. Soot is a great insulator. A 1/8" layer of soot is equal to 1"+ of fiberglass insulation. This seriously restricts heat transfer & reduces efficiency. At that age make sure they check the heat exchanger well at each service.