    CO PPM in exaust on Bryant 350MAV

    Question. I ws on a Bryant 350MAV 90% furnace yesterday and the flames looked funny so I took a reading in the exhaust and it was 1392 PPM. Secondary heat exchanger is bad. Roll out switch was not tripped but the burner box was extremely hot. I had my own business in Minnesota and by code you are suppose to red tag furnace. So I called Bryant here in Indiana nd they told me as long a it is not entering into living area I should leave it on for them to have heat. Of course I was shocked about this and felt uncomortable but the other tech said to leave it on for them also. So I left it on even though I was uncomfortable with this. The other tech said since Bryant had a enclosed burner compartment and the inake was vented outside it was ok to leave furnace running.

  2. #2
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    5,659
    Did you use a CO meter in the living space to make sure CO wasn't entering the living space.

  3. #3
    Join Date
    May 2007
    Location
    somewhere between heaven and hell
    Posts
    955
    Yes I did 0 PPM in living space.

  4. #4
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    5,016
    Quote Originally Posted by mrlighturfire View Post
    So I called Bryant here in Indiana nd they told me as long a it is not entering into living area I should leave it on for them to have heat.
    Is Bryant willing to supply you with a letter stating that 1394 ppm of CO is OK, and the unit is safe to operate? I doubt it.

    I would also have the home owner put in writing the fact that you want to red tag the unit until it is fixed, but they are authorizing you to leave it operating knowing the dangers.

    Even then, who knows what the lawyers would do, if anything happens.
    Instead of learning the tricks of the trade, learn the trade.

  5. #5
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    5,659
    Quote Originally Posted by rundawg View Post
    Is Bryant willing to supply you with a letter stating that 1394 ppm of CO is OK, and the unit is safe to operate? I doubt it.

    I would also have the home owner put in writing the fact that you want to red tag the unit until it is fixed, but they are authorizing you to leave it operating knowing the dangers.

    Even then, who knows what the lawyers would do, if anything happens.
    X2

  6. #6
    Join Date
    May 2007
    Location
    somewhere between heaven and hell
    Posts
    955
    I told the homeowner this and how I felt about this and of course homeowner had no CO detectors in the house. Bryant here in Indiana I am kinda fed up with them. I had a secondary plugged up couple weeks ago and they won't honor the warranty on a plugged secondary unless it is rusted out. They said you should have abulletin about this at your shop which we dobut haven't had time to read this yet. But I will ths weekend.

  7. #7
    Join Date
    May 2007
    Location
    somewhere between heaven and hell
    Posts
    955
    For now on this is what I will do with the homeowner. And document it at the same time. This is ust uncomfortable.

  8. #8
    Join Date
    May 2007
    Location
    somewhere between heaven and hell
    Posts
    955
    I am going to find mydocuments from NCI that acks m statement up.

  9. #9
    Join Date
    May 2007
    Location
    somewhere between heaven and hell
    Posts
    955
    Having trouble wih my keyboard guess I should red tag my keyboard while I am at it.

  10. #10
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,763
    If your state doesn't have laws/regs requiring you to disable the furnace. Then turn the switch off. note it on your invoice that you did so. leave a copy of your readings with the invoice. Verbally explain why its unsafe to the customer, and tell them you turned/left the service switch in the off position. note on your invoice that you explained the dangers to the customer, and that you informed them that the power was turned off. get their signature. If they turn it back on later. You have your proof you explained the dangers, and left the furnace turned off.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #11
    Join Date
    Jul 2012
    Location
    Cincinnati ohio
    Posts
    233
    Quote Originally Posted by beenthere View Post
    If your state doesn't have laws/regs requiring you to disable the furnace. Then turn the switch off. note it on your invoice that you did so. leave a copy of your readings with the invoice. Verbally explain why its unsafe to the customer, and tell them you turned/left the service switch in the off position. note on your invoice that you explained the dangers to the customer, and that you informed them that the power was turned off. get their signature. If they turn it back on later. You have your proof you explained the dangers, and left the furnace turned off.
    I agree. A secondary h/x with the polypropolene failure is the same as a hole or crack in a primary. The unit should be redtagged and the gas and electric turned off. it is our company policy anyway. ALWAYS COVER YOUR ASS!

  12. #12
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    6,914
    According to ANSI standards, you must shut down or disable any vented appliance that produces over 400 ppm of CO.

    Shut it off, hang a red tag, and notate your readings on the ticket and have owner sign ticket. If the owner turns it back on, that's not your problem.

    Sounds like your Bryant people need some info on industry standards as they relate to CO.

  13. #13
    Join Date
    Dec 2011
    Location
    somewhere between here and there
    Posts
    478
    pic taken from 8 yr old bryant 340AAV042080Name:  photo.jpg
Views: 435
Size:  75.6 KB


    Please, Please Please......keep the Factory Smoke in the Wires!!!!!


    Is it Rum'Oclock yet???

Page 1 of 4 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event