Results 1 to 5 of 5
  1. #1
    Join Date
    Jan 2013
    Location
    Central Arkansas
    Posts
    127
    Post Likes

    chasing duct work blockage

    I work in a hospital, a few days ago we had a interesting coincidence we had to test a fire door later in the day we had a comlaint of no cooling in some areas. we found we were not getting air past a certian area so we started looking at smoke and fire dampers and fornd the a airline blown off a air actuator. Now my question is there a better way look for a blockage or do you do the same thing we had to do just start moving celing tile and chasing the duct work?

  2. #2
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,304
    Post Likes
    Thread relocated to "Tech to Tech"

  3. #3
    Join Date
    Jan 2013
    Location
    Central Arkansas
    Posts
    127
    Post Likes
    thanks chris I realised afterwords I posted in the wrong place

  4. #4
    Join Date
    Jan 2013
    Posts
    21
    Post Likes
    With Pneumatic there is little you can do but to trace out the lines to find the failure with a BAS system with the appropriate points you can find the location through point failures or duct pressure readings if this is monitored or temp sensor monitors. Also if it is a hybrid system you may be able to use the BAS to pinpoint the point of failure.

  5. #5
    Join Date
    Feb 2005
    Location
    In a van by the river
    Posts
    624
    Post Likes
    I measure duct static pressure with a manometer every 20 ft or so until a general section is located with a restriction. Then I remove ceiling grids to check for dampers/ actuators in that vicinity.
    ## + years in the field never made you a know-it-all This industry is far more diverse than you are

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365