help! started unit with opening a dry condensor
help 2 hours ago i started unit with my new skills i learned on the job i pulled a vacuum and i forgot to open my vavles on a dry cond with nitogen in it i put freon in opened the valves and i forgot it was nitrogen in it not freon r-22 ...what do i do ? do i reclaim and pull a new vacuum and then charge properly .. and do i do it immediatly?
-
01-18-2013, 08:22 PM #2
-
01-18-2013, 08:31 PM #3
Regular Guest
- Join Date
- Feb 2011
- Posts
- 10
i charged it, it has freon ,but the nitrogen from the condensor is also in it mixed? i was in a hurry and screwed up
-
01-18-2013, 08:35 PM #4
Regular Guest
- Join Date
- Feb 2011
- Posts
- 10
Do I need shut it down asap?
-
01-18-2013, 08:51 PM #5.”No law ever prevented a crime.”
~Anonymous
-
01-18-2013, 09:08 PM #6
Regular Guest
- Join Date
- Feb 2011
- Posts
- 10
I ran it for for an hour or so and then the t stat at 75 its been 4 hours now
-
01-18-2013, 09:15 PM #7
Uh oh
-
01-18-2013, 09:18 PM #8
-
01-18-2013, 09:19 PM #9
You need to empty the system and start over.
The R22 in there is no good now
Open both king valves and leave them open , you are done using those now.
Using the shrader valves , reclaim the bad gas , vacuum it down , add new R22 , done .
-
01-18-2013, 09:19 PM #10
-
01-18-2013, 09:20 PM #11
Is this for real? Between this and fengHVAC I'm starting to think someone is pranking the members.
-
01-18-2013, 09:22 PM #12
With 420 in the username it is probably easy to forget something like that.
-
01-18-2013, 09:24 PM #13
Do as stated above ASAP!
Do not operate the system until you have recovered contaminated charge, pulled a vacuum to below 500 microns, and weighed in the charge using the correct refrigerant.
Failing to do so will cause that system to fail VERY soon!


Reply With Quote