    Confused help! started unit with opening a dry condensor

    help 2 hours ago i started unit with my new skills i learned on the job i pulled a vacuum and i forgot to open my vavles on a dry cond with nitogen in it i put freon in opened the valves and i forgot it was nitrogen in it not freon r-22 ...what do i do ? do i reclaim and pull a new vacuum and then charge properly .. and do i do it immediatly?

  2. #2
    Join Date
    May 2000
    Location
    anywhere my RV is
    Posts
    18,754
    Post Likes
    Quote Originally Posted by zman420 View Post
    help 2 hours ago i started unit with my new skills i learned on the job i pulled a vacuum and i forgot to open my vavles on a dry cond with nitogen in it i put freon in opened the valves and i forgot it was nitrogen in it not freon r-22 ...what do i do ? do i reclaim and pull a new vacuum and then charge properly .. and do i do it immediatly?
    yep, your screwed. Reclaim, pull a new vacuum......CHARGE THE SYSTEM.....open the valves THEN start it up.

    how long did it run without freezone in it?
    Why am I the only naked person at this gender reveal party

  3. #3
    Join Date
    Feb 2011
    Posts
    10
    Post Likes
    Thread Starter
    i charged it, it has freon ,but the nitrogen from the condensor is also in it mixed? i was in a hurry and screwed up

  4. #4
    Join Date
    Feb 2011
    Posts
    10
    Post Likes
    Thread Starter
    Do I need shut it down asap?

  5. #5
    Join Date
    May 2000
    Location
    anywhere my RV is
    Posts
    18,754
    Post Likes
    Quote Originally Posted by zman420 View Post
    Do I need shut it down asap?
    YES !!!!!!!!!!!!!!!!!!!!! your running this thing with R-22 AND Nitrogen in the system??? How long has this been running???

    Reclaim whatever you have in there, pull a vacuum, recharge and restart and hope the system last a few years
    Why am I the only naked person at this gender reveal party

  6. #6
    Join Date
    Feb 2011
    Posts
    10
    Post Likes
    Thread Starter
    I ran it for for an hour or so and then the t stat at 75 its been 4 hours now

  7. #7
    Join Date
    Apr 2012
    Location
    Cleveland
    Posts
    744
    Post Likes
    Uh oh

  8. #8
    Join Date
    May 2000
    Location
    anywhere my RV is
    Posts
    18,754
    Post Likes
    Quote Originally Posted by Hvac216 View Post
    Uh oh
    that would be an understatement LOL, i think Zman may have killed the patient. This can't be good.
    Why am I the only naked person at this gender reveal party

  9. #9
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    You need to empty the system and start over.

    The R22 in there is no good now

    Open both king valves and leave them open , you are done using those now.

    Using the shrader valves , reclaim the bad gas , vacuum it down , add new R22 , done .

  10. #10
    Join Date
    May 2000
    Location
    anywhere my RV is
    Posts
    18,754
    Post Likes
    Quote Originally Posted by Hvac216 View Post
    Uh oh
    that would be an understatement LOL, i think Zman may have killed the patient. This can't be good.
    Why am I the only naked person at this gender reveal party

  11. #11
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,430
    Post Likes
    Is this for real? Between this and fengHVAC I'm starting to think someone is pranking the members.

  12. #12
    Join Date
    Apr 2012
    Location
    Cleveland
    Posts
    744
    Post Likes
    With 420 in the username it is probably easy to forget something like that.

  13. Likes Turtleman liked this post.
  14. #13
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    Do as stated above ASAP!

    Do not operate the system until you have recovered contaminated charge, pulled a vacuum to below 500 microns, and weighed in the charge using the correct refrigerant.

    Failing to do so will cause that system to fail VERY soon!

  15. #14
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Quote Originally Posted by Hvac216 View Post
    With 420 in the username it is probably easy to forget something like that.
    I'm sure that's just dinner time lol

  16. #15
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    Zman,

    I was checking your previous posts and you stated you've been in the trade for 25 years? You were inquiring about a Florida contractor license.

    http://hvac-talk.com/vbb/showthread.php?t=750461

    I understand accidents happen but with that many years experience, you should know exactly what to do!

    I'm kinda confused.

  17. #16
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Relatively easy to seperate the two in a cylinder.

    Oh and did this happen before or after 4:20pm on Friday?

    Ill go ahead and admit doing the same thing before. I thought I read serial and saw 0911 and thought I had a older 2009 unit. Oops.

  18. #17
    Join Date
    May 2000
    Location
    anywhere my RV is
    Posts
    18,754
    Post Likes
    not me, the guy has to be a troll, 25 years and he pulls this???

    something is definitely not right here
    Why am I the only naked person at this gender reveal party

  19. #18
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    I was trying to put it nicely. Haha. That post was from 2011...so he should have 27 years experience now!

    When are people going to learn? The key is to be humble and truthful. If you possess these things, you'll gain more education from this site than you've ever dreamed of! I sure know I have.

    But if you do the opposite, we aren't so willing to help and you will get run off quickly.

  20. #19
    Join Date
    Feb 2011
    Posts
    10
    Post Likes
    Thread Starter
    april 20 is my birthday and i drive a 350 z and there is no excuse for i what i did but being in a hurry before dark hit , i went back and killed the breaker , i will pull a new vacuum for a good hour or so and recharge according the mfg specs ,thanks for the helpful comments ,and to the smart ass ,im sure you have never ever ever made mistake ,and if not ,i hope you do one day......lesson learned thanks

  21. #20
    Join Date
    Dec 2004
    Location
    Caledonia WI
    Posts
    1,962
    Post Likes
    See.....! now some people are already suffering the repercussions from chasing Feng away. Had he been here to lend his master tutelage in the hvac, this poor soul would never have been in this predicament in the first place.

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •