Page 1 of 4 1234 LastLast
Results 1 to 13 of 46
  1. #1
    Join Date
    Feb 2011
    Posts
    10
    Post Likes

    Confused help! started unit with opening a dry condensor

    help 2 hours ago i started unit with my new skills i learned on the job i pulled a vacuum and i forgot to open my vavles on a dry cond with nitogen in it i put freon in opened the valves and i forgot it was nitrogen in it not freon r-22 ...what do i do ? do i reclaim and pull a new vacuum and then charge properly .. and do i do it immediatly?

  2. #2
    Join Date
    May 2000
    Location
    Rochester, NY, USA
    Posts
    16,359
    Post Likes
    Quote Originally Posted by zman420 View Post
    help 2 hours ago i started unit with my new skills i learned on the job i pulled a vacuum and i forgot to open my vavles on a dry cond with nitogen in it i put freon in opened the valves and i forgot it was nitrogen in it not freon r-22 ...what do i do ? do i reclaim and pull a new vacuum and then charge properly .. and do i do it immediatly?
    yep, your screwed. Reclaim, pull a new vacuum......CHARGE THE SYSTEM.....open the valves THEN start it up.

    how long did it run without freezone in it?
    "THE LIONS DON'T CARE ABOUT THE OPINIONS OF THE SHEEP"

    Scott Isreal
    Coward County Sheriff ​

  3. #3
    Join Date
    Feb 2011
    Posts
    10
    Post Likes
    Thread Starter
    i charged it, it has freon ,but the nitrogen from the condensor is also in it mixed? i was in a hurry and screwed up

  4. #4
    Join Date
    Feb 2011
    Posts
    10
    Post Likes
    Thread Starter
    Do I need shut it down asap?

  5. #5
    Join Date
    May 2000
    Location
    Rochester, NY, USA
    Posts
    16,359
    Post Likes
    Quote Originally Posted by zman420 View Post
    Do I need shut it down asap?
    YES !!!!!!!!!!!!!!!!!!!!! your running this thing with R-22 AND Nitrogen in the system??? How long has this been running???

    Reclaim whatever you have in there, pull a vacuum, recharge and restart and hope the system last a few years
    "THE LIONS DON'T CARE ABOUT THE OPINIONS OF THE SHEEP"

    Scott Isreal
    Coward County Sheriff ​

  6. #6
    Join Date
    Feb 2011
    Posts
    10
    Post Likes
    Thread Starter
    I ran it for for an hour or so and then the t stat at 75 its been 4 hours now

  7. #7
    Join Date
    Apr 2012
    Location
    Cleveland
    Posts
    744
    Post Likes
    Uh oh

  8. #8
    Join Date
    May 2000
    Location
    Rochester, NY, USA
    Posts
    16,359
    Post Likes
    Quote Originally Posted by Hvac216 View Post
    Uh oh
    that would be an understatement LOL, i think Zman may have killed the patient. This can't be good.
    "THE LIONS DON'T CARE ABOUT THE OPINIONS OF THE SHEEP"

    Scott Isreal
    Coward County Sheriff ​

  9. #9
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    4,421
    Post Likes
    You need to empty the system and start over.

    The R22 in there is no good now

    Open both king valves and leave them open , you are done using those now.

    Using the shrader valves , reclaim the bad gas , vacuum it down , add new R22 , done .

  10. #10
    Join Date
    May 2000
    Location
    Rochester, NY, USA
    Posts
    16,359
    Post Likes
    Quote Originally Posted by Hvac216 View Post
    Uh oh
    that would be an understatement LOL, i think Zman may have killed the patient. This can't be good.
    "THE LIONS DON'T CARE ABOUT THE OPINIONS OF THE SHEEP"

    Scott Isreal
    Coward County Sheriff ​

  11. #11
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,403
    Post Likes
    Is this for real? Between this and fengHVAC I'm starting to think someone is pranking the members.

  12. #12
    Join Date
    Apr 2012
    Location
    Cleveland
    Posts
    744
    Post Likes
    With 420 in the username it is probably easy to forget something like that.

  13. #13
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    Do as stated above ASAP!

    Do not operate the system until you have recovered contaminated charge, pulled a vacuum to below 500 microns, and weighed in the charge using the correct refrigerant.

    Failing to do so will cause that system to fail VERY soon!

Page 1 of 4 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.