help! started unit with opening a dry condensor
help 2 hours ago i started unit with my new skills i learned on the job i pulled a vacuum and i forgot to open my vavles on a dry cond with nitogen in it i put freon in opened the valves and i forgot it was nitrogen in it not freon r-22 ...what do i do ? do i reclaim and pull a new vacuum and then charge properly .. and do i do it immediatly?
-
 Originally Posted by zman420
help 2 hours ago i started unit with my new skills i learned on the job i pulled a vacuum and i forgot to open my vavles on a dry cond with nitogen in it i put freon in opened the valves and i forgot it was nitrogen in it not freon r-22 ...what do i do ? do i reclaim and pull a new vacuum and then charge properly .. and do i do it immediatly?
yep, your screwed. Reclaim, pull a new vacuum......CHARGE THE SYSTEM.....open the valves THEN start it up.
how long did it run without freezone in it?
"THE LIONS DON'T CARE ABOUT THE OPINIONS OF THE SHEEP"
Scott Isreal
Coward County Sheriff
-
i charged it, it has freon ,but the nitrogen from the condensor is also in it mixed? i was in a hurry and screwed up
-
Do I need shut it down asap?
-
 Originally Posted by zman420
Do I need shut it down asap?
YES !!!!!!!!!!!!!!!!!!!!! your running this thing with R-22 AND Nitrogen in the system??? How long has this been running???
Reclaim whatever you have in there, pull a vacuum, recharge and restart and hope the system last a few years
"THE LIONS DON'T CARE ABOUT THE OPINIONS OF THE SHEEP"
Scott Isreal
Coward County Sheriff
-
I ran it for for an hour or so and then the t stat at 75 its been 4 hours now
-
-
 Originally Posted by Hvac216
Uh oh
that would be an understatement LOL, i think Zman may have killed the patient. This can't be good.
"THE LIONS DON'T CARE ABOUT THE OPINIONS OF THE SHEEP"
Scott Isreal
Coward County Sheriff
-
You need to empty the system and start over.
The R22 in there is no good now
Open both king valves and leave them open , you are done using those now.
Using the shrader valves , reclaim the bad gas , vacuum it down , add new R22 , done .
-
 Originally Posted by Hvac216
Uh oh
that would be an understatement LOL, i think Zman may have killed the patient. This can't be good.
"THE LIONS DON'T CARE ABOUT THE OPINIONS OF THE SHEEP"
Scott Isreal
Coward County Sheriff
-
Is this for real? Between this and fengHVAC I'm starting to think someone is pranking the members.
-
With 420 in the username it is probably easy to forget something like that.
-
Do as stated above ASAP!
Do not operate the system until you have recovered contaminated charge, pulled a vacuum to below 500 microns, and weighed in the charge using the correct refrigerant.
Failing to do so will cause that system to fail VERY soon!