Freeze Stat trips, when OA temp drops to 30F, but zone is need of cooling.
Hi, I looked all over this forum and didnt find my answer, so here is my question.
My equipment (AHU) trips on freeze stat and shuts down the unit, I do have a few AHU's that back each other up, but here's what going on. I have a zone that is always hot and needs cooling, OA temp is in the low 30's, and OA damper is modulated and is open 100% to try to satisfy the zone after a few minutes or so, the freeze stat trips and unit is shutdown. Freeze stat is located after the HW coil, but before the CHW Coil. Freeze stat is set to trip at 33F
What can be done to prevent the trips in the future? I have full admin rights to the BMS, and can change the coding as I please, would it be logical to override the OA dampers to go to its minimum position, if the OA temp dropps below 35F?
But then thinking about this, wouldnt it start to open the CHW valve, and in doing so, it sends a start signal to the Chiller plant and start up the chillers when OA temp is 30F? BMS has chillers to be locked out if the OA temp drops below 45F. So chillers wouldnt start anyway. I guess what im asking is, what is the right thing to do, I know the Freeze stat is to protect the coil, but if the space is in need of cooling, then what do i do?
Thanks in advance.
-
01-18-2013, 09:16 AM #2
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,108
Check the control drawing's "sequence of operation". Your answer should be there. If my buildings had air side economizing I would tell you what mine said, but I have water side economizing.
-
01-18-2013, 09:30 AM #3
Control your dampers via the mixed air temp when economizing.
-
01-18-2013, 09:34 AM #4
Regular Guest
- Join Date
- May 2007
- Location
- City That Never Sleeps
- Posts
- 66
This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.
You can find the rules for posting and qualifications here.
Additional infractions may result in loss of posting privileges.
Last edited by jpsmith1cm; 01-18-2013 at 06:40 PM. Reason: non AOP member
-
01-18-2013, 02:58 PM #5
-
01-18-2013, 04:24 PM #6
-
01-18-2013, 05:20 PM #7
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,108
Please realize that just because you CAN access the BMS and make changes, that doesn't mean you SHOULD.
-
01-18-2013, 06:41 PM #8
Trane Tech NYC
This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.
You can find the rules for posting and qualifications here.
Additional infractions may result in loss of posting privileges.
-
01-18-2013, 08:54 PM #9
Professional Member
- Join Date
- Mar 2008
- Location
- Kitchener, Ontario
- Posts
- 491
-
01-18-2013, 10:38 PM #10
Professional Member*
- Join Date
- Feb 2006
- Location
- Atlanta,GA.
- Posts
- 729
can you set the discharge air temp? if you set it at 45 that should cool the space and the heating coil should open to bring the temp up to keep from tripping. check to make sure your hw valve is opening.
-
01-19-2013, 08:33 PM #11
This is where I'd be looking to go with it.
If the freeze-stat is tripping then the air is obviously too cold and will freeze the heating coil if OA is allowed to continue to be used for any length of time. I see it all of the time.
No one wants to be breathing air that is that cold anyway, makes for an uncomfortable time.
...RonRoof Rat
-