    Victory VF-1 stand up reach in single stainless door freezer
    Compressor is AFE13C3E-IAA-901 copeland
    complaint , wont hold temp , imagine that
    200 high , 5 low , 50 deg inside box ( no product ) , pullin 12 amps
    Feel drier , its warm incoming , and cold right where the cap tubes are brazed into the stub. I knew then its got to be clogged. Normally they are warm a couples inches up cap tube before they get cold.
    Cut it out , then cut it open , sure enough the dessicant beads had busted through the screen and clogged it up.
    Install new drier , amazingly caps still looked good , I could blow through both caps just fine , braze back in.
    Both coils clean
    Pull her down , Weigh in 10 OZ 404
    Fire it up , I have 210 high , 28 low , pulling 9.2 amps , evap frosting evenly
    10 min later the evap fan comes on , starts falling from 50 degrees to 45
    210 high , 25 low 9 amps , cant measure Sh Sc , cant find my dam clamp on
    Few minutes later for no reason ..... compressor shuts down.
    CRAP
    Few minutes later hear "click" hmmmmmmm Click
    Throw infared thermometer on shell , reads 145 deg , seems normal , but whatever , Get out ice , cool it down.
    Runs again 10 minutes , evap frosting nicely , fan kicks on
    Few min later compr shuts down.
    Crap
    Before I beat it with a hammer , I pack up and go home.
    Why would it shut down when everything is going so well ??
    Oct 2005
    B.C. Canada
    click hmmmmmmmm click cause it didnt equalize.... why it shut down, not sure, was it the ol that opened?? if so, yah its weak from running too hot while cap tube was plugged...
    just a guess, had a few beerz... first day off call after a week :-)
    Oct 2005
    B.C. Canada
    Change all the start $#it to be safe
    Virginia
    I threw 3n1 on it , same thing
    It would shut down after 10 min , then after that , the 3n1 would click off a few seconds later on its own OL
    Dec 2008
    New York, ny
    Your amps are high just check the model number on the net, you should be around 6.4. So your overload is actually doing its job.
    Sent from my SGH-T999 using Tapatalk 2
    Oct 2005
    B.C. Canada
    whats fla?? whats the 3in1 rated at?? u have yer meter on it when she craps out?? somthin makin amps spike?? non condensables i dunno...
    Oct 2005
    B.C. Canada
    thankx grkmano.. beat me to it
    Comp gettin tight?? Doesnt sound over charged
    Dec 2008
    New York, ny
    Exactly you probably had no oil return and now the compressor over working to pump.
    Oct 2005
    B.C. Canada
    Quote Originally Posted by grkmano View Post
    yup.. new pump.... crappy deal for your custumer , but thats life.. probley originally caused by lack of maint. wus the cond plugged??
    Virginia
    cond was clean , the owner cleans them himself , hes a long time restaurant owner.
    I didnt even think about oil return issues while it was plugged up ...
    Yea I see now that compressor has a rating of 6.4 ... son of a
    Its probably slightly scored up inside , just enough to run
    The problem was the drier failed , the screen had a tiny rip , let all the dessicant out
    Virginia
    is this a job for Supco 88 ... or just go ahead with new compr
    Oct 2005
    B.C. Canada
    Well, we all know what has to happen now......
    Ps why isnt anyone helping me with this -150 lab freezer... dammit
    Oct 2011
    Chicagoland Area
    Quote Originally Posted by coolerik View Post
    Cause you're the guinea pig