First Company Brand
Model# WSVC048N-2LH-FT
Put in last June, only used a couple of times, it's in a vacation condo.
Would like to see if anyone could give me a little advise on flushing the water condensing coil on this unit.
I got the call to replace the control board on this unit, did that but found another issue. I found the unit shutting down because of the discharge line getting to hot, sensor is on the liquid line coming out of the compressor, just before the reversing valve. My water inlet temp is 70-71deg, but the water outlet temp is hitting 100+deg before the board shuts it down. I pulled the inlet water line off to see maybe it had a clogged screen, no screen, but got rust and gunk out when it back washed from the hose being removed. I removed the water outlet hose same thing. I have tried to shock the unit in hopes the clog will dislodge, but have not had any luck.
What do I need to do next?
-
01-23-2013, 04:38 PM #2
Regular Guest
- Join Date
- May 2005
- Posts
- 148
This happened to me when I was running open loop except it was the reverse. Unit was shutting down because it got too cold from extremely low flow. The manufacturer (FHP) recommended using Muriatic acid. So I tried flushing in both directions, then I eventually started letting it soak for long periods of time and blasting it out with compressed air regulated down. It took me all day to get clean water out of it. What a hassle. After that I went closed loop with good, clean water and methanol. No problems since.