Results 1 to 12 of 12
  1. #1

    Customer went all out

    We didn't build it we just work on it. Customer had 3 80ton TS chillers. Problem was they have two motors to be cooled and the way it is piped one chiller per motor with the third on standby if one of the others drops out. No bypasses or anything so they were running 60 degree chilled water and in summer the TSs hated life. I have mentioned these before but the chilled water upgrade is near completion. They went all out.
    Click image for larger version. 

Name:	ImageUploadedByTapatalk1358441241.715553.jpg 
Views:	361 
Size:	54.8 KB 
ID:	347791
    Click image for larger version. 

Name:	ImageUploadedByTapatalk1358441181.181388.jpg 
Views:	345 
Size:	61.0 KB 
ID:	347781
    Here are the old TSs^
    they built a shelter over the controls with electric and lighting
    Click image for larger version. 

Name:	ImageUploadedByTapatalk1358441312.166029.jpg 
Views:	319 
Size:	44.6 KB 
ID:	347801
    Here is the new 225 ton Trane addition
    Click image for larger version. 

Name:	ImageUploadedByTapatalk1358441513.080029.jpg 
Views:	307 
Size:	66.1 KB 
ID:	347811
    They put in a 8000 gallon chilled water tank. They never had enough of a cushion. When the motors would unload the chillers would fall on their face. Then when they loaded the chillers would maybe catch up in time for unloading.
    Click image for larger version. 

Name:	ImageUploadedByTapatalk1358441665.614409.jpg 
Views:	276 
Size:	56.3 KB 
ID:	347821
    We even have a panel where we can see what the motors are doing
    Click image for larger version. 

Name:	ImageUploadedByTapatalk1358441736.210374.jpg 
Views:	280 
Size:	54.0 KB 
ID:	347831
    And how things are cooling
    Click image for larger version. 

Name:	ImageUploadedByTapatalk1358441772.925804.jpg 
Views:	270 
Size:	48.8 KB 
ID:	347841

    The new setup is getting started soon. Chilled water setpoint will now drop to 50. Chillers will be happy. And the motors won't Condensate with bypass valves installed. Life for us will be a little easier with the Trane on primary so the TS machines can be brought back up to snuff.

  2. #2
    Join Date
    Aug 2012
    Posts
    1,579
    What kind of motors are they cooling?
    Certified parts changer.

  3. #3
    Quote Originally Posted by toocoolforschool View Post
    What kind of motors are they cooling?
    Med size GE motors here a rotor
    Click image for larger version. 

Name:	ImageUploadedByTapatalk1358443991.843681.jpg 
Views:	176 
Size:	63.2 KB 
ID:	347861
    I have an old thread titled "big electric motor" that had some more stuff in it.

  4. #4
    Join Date
    Aug 2012
    Posts
    1,579
    Good stuff, Amazing the amount of cooling it needs though.
    Certified parts changer.

  5. #5
    Join Date
    Aug 2012
    Posts
    1,579
    Good stuff, Amazing the amount of cooling it needs though.
    6000 amps per leg at 125%, holly molly.
    Certified parts changer.

  6. #6
    Quote Originally Posted by toocoolforschool View Post
    Good stuff, Amazing the amount of cooling it needs though.
    They keep upping the bar on the motors. If you look at these they are running at 125% on that screen. They were rebuilt to run that high. They want to raise it up some more which was part of the push. The biggest motors at this location are on nasty swamp coolers still. They are maxed out and have to slow down in summer to below 80%. We changed over a swamp cooler on a downstream mill to two RTACs chilling 100% outside air to 60 and the never have to slow down. Cool temps mean happy motors, happy motors make big money.

  7. #7
    Join Date
    Aug 2009
    Location
    Prattville,Alabama
    Posts
    1,138
    Hopefully changing that one swamp cooler over to a chiller will motivate them to change over the others. Sounds like you are happy, too. Thanks for sharing this.

  8. #8
    Quote Originally Posted by Nuclrchiller View Post
    Hopefully changing that one swamp cooler over to a chiller will motivate them to change over the others. Sounds like you are happy, too. Thanks for sharing this.
    Each mill acts like a separate company. The swamp cooler reversing mill really digs our twin RTAC setup at the finish mill for it's capacity and reliability. The mill in today's post was partial in house and a local company but it will work great and we service it so were happy. This place plans for the future so much if you notice the pit the chillers sit in was built a long time ago. There was always a spot for this RTAC: concrete runners, studs, and conduit put in ten plus years ago. On chilled water loops they put in stubs and valves for rental machines even incase of catastrophic chiller failure. This place is the service techs garden of Eden most of the time.

  9. #9
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,064
    Happy motors= big $$= happy customer= we get to keep account for long long time.

  10. #10
    Join Date
    Aug 2012
    Posts
    1,579
    It's a papermill? This is good stuff I like big machines, those paper mills are incredible the way they maximize each log and cut them in seconds.
    Certified parts changer.

  11. #11
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,064
    Quote Originally Posted by toocoolforschool View Post
    It's a papermill? This is good stuff I like big machines, those paper mills are incredible the way they maximize each log and cut them in seconds.
    Aluminum. It's a gear head wet dream. A lot of amazing machines everywhere.

  12. #12
    Better yet, Beer can aluminum. Clean process. Not like diamond plate or material rolling aluminum that are filth to the max.

Posting Permissions