Results 1 to 8 of 8
Thread: need Armstrong igniter advice
-
02-04-2013, 06:56 PM #1
need Armstrong igniter advice
Looking at an Armstrong 80 GUJ100D12-2B furnace that's not igniting but I am unfamiliar with the hot surface ignition system. Just trying to determine if it's the gas valve or igniter, What kind of voltage should I be seeing on the igniter leads? I'm getting 6 volts.
-
02-04-2013, 07:12 PM #2
Is there a smart valve on that furnace?
-
02-04-2013, 07:47 PM #3
-
02-04-2013, 08:16 PM #4
Hey rundawg, do you have any sort of file on ohm reading for different ignitors? I just would like something to save or else I forget.
-
02-04-2013, 08:46 PM #5
-
02-04-2013, 08:51 PM #6
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,216
The resistance of a Norton silicon igniter used in the Q3450 or Q 3480 pilot assemblies, when new and
cold, will be between 3 and 4 Ohms (average 3.7 Ohms) as the igniter ages the resistance will increase. When
its resistance reaches 10 Ohms the igniter should be replaced
anyone have a better cut & paste about the ignitors
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
02-04-2013, 09:22 PM #7
-
02-05-2013, 11:34 AM #8
That helps, thanks guys.