    18 SEER Amana Heat Pump - Loud Grinding Noise on Startup

    Hi everyone,

    I have a < 1 year old 18 SEER Amana Heat Pump (this guy here: http://www.amana-hac.com/Home/Produc...5/Default.aspx ).

    It was installed last year - end of January 2012.

    For the past couple weeks after the defrost cycle it's been kicking back on with an insanely loud noise.

    It wakes us up everytime this happens, which is about once an hour.

    I just recorded it and posted it to youtube here (the grinding noise starts 20 seconds in):

    http://www.youtube.com/watch?v=LOWRIRLNTsM

    It was nighttime so there's not much to see, but you can hear it clearly. Please can you guys take a listen and let me know if this is normal operation? My contractor seems to think there's no problem, but I can't imagine this incredibly loud noise is normal.

    I really appreciate it.

    Kevin

  2. #2
    Join Date
    Oct 2005
    Location
    Pacific Northwest
    Posts
    2,267
    Your technician can verify that the defrost cycle is terminating when it's supposed too. If a defrost cycle carries on unnecessarily, excessive pressures can cause a noisy compressor when the defrost cycle terminates. If the cycle is terminating correctly then there really isn't much that can be done. The higher seer equipment tends to carry on a bit noise wise when defrosting.

  3. #3
    Join Date
    Jan 2013
    Location
    White Plains, NY
    Posts
    6
    Thanks for the response crmont.

    Your comment makes sense - I've noticed that as the temperature drops, the duration, volume, and overall jarring DECREASES - to the point where it does not wake us up. Which makes me think that the defrost cycle is carrying on unnecessarily at the higher temps, and is working correctly at lower temps.

    It happens every 30 minutes. I timed it last night. Is there a way to control that timing? at the thermostat?

    I have a VisionPro IAQ. I couldn't find an appropriate setting last night.

    Thanks for the help.
    Kevin

  4. #4
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,371
    Quote Originally Posted by kmkuntz View Post
    Thanks for the response crmont.

    Your comment makes sense - I've noticed that as the temperature drops, the duration, volume, and overall jarring DECREASES - to the point where it does not wake us up. Which makes me think that the defrost cycle is carrying on unnecessarily at the higher temps, and is working correctly at lower temps.

    It happens every 30 minutes. I timed it last night. Is there a way to control that timing? at the thermostat?

    I have a VisionPro IAQ. I couldn't find an appropriate setting last night.

    Thanks for the help.
    Kevin
    The defrost cycle time is controlled by the defrost board within the heat pump itself, and your technician should be able to adjust the frequency of defrost cycles (typically every 30/60/90 min). I believe the default on Goodman/Amana is 30 min so that is likely where they left it.

    Another reason demand defrost is preferred to time/temp method which produces unnecessary defrost cycles. Your Amana heat pump should have the "SmartShift" feature that Goodman units do, which delays the compressor start-up at defrost initiation/termination. This should be enabled from the factory according to Goodman documentation, however, so this may not be relevant.

  5. #5
    Join Date
    May 2008
    Location
    Missouri
    Posts
    3,543
    Have your service person put defrost timer on longer interval. Most likely 30 minutes is too short. We set ours at 90 minutes. See if that helps.

  6. #6
    Join Date
    Jan 2013
    Location
    White Plains, NY
    Posts
    6
    Great info guys. I'll ask my service tech to increase the defrost cycle to 90 min, and ask him if the SmartShift feature is enabled and working.

    Thanks for the help. Really appreciate it.

    Kevin

  7. #7
    Join Date
    Oct 2005
    Location
    Pacific Northwest
    Posts
    2,267
    As evident by the video; snow on the ground means the timer should be on a 30 minute check. The hp had terminated defrost and was still equalizing pressure when the compressor started. That means the quiet shift function is already enabled. Good luck.

  8. #8
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    2,153
    How long is the compressor off after the reversing valve is shifted? The "quietshift" timing for the compressor can be changed on the control board to delay the compressor so the pressures equalize before the compressor starts. I know the 13seer units have this on the new board and a delay kit can be added to systems with the old board. It sounded like the system was still equalizing when the compressor started and it was trying to pump liquid on startup thus the noise and when the liquid clears it quiets down.
    ...

  9. #9
    Join Date
    Jan 2013
    Location
    White Plains, NY
    Posts
    6
    The compressor is off for about 20 seconds after the reversing valve shifts. The delay kit that you mention - is that the DFTD-1? I read about it in another post on this forum. I'll call my service tech and see if he can increase that time a bit, either with this delay kit or (hopefully) via the board itself.

    The noise has been absent since we've had much colder temps over the last couple days. Strange that it only grinds like that when the temps are 30-40.

    Thanks everyone for all the responses.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event