Results 1 to 13 of 16
-
01-16-2013, 07:59 PM #1
-
01-16-2013, 08:03 PM #2
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
You can replace just that plate. I just did one along with the inducer bracket. Mine was the 48 DJE 006. Just getting the last season out of it before it's replaced next fall.
-
01-16-2013, 08:14 PM #3
We just replaced 28 heat exchangers on this school. They will all be replaced within 5 yrs.
-
01-16-2013, 08:52 PM #4
Looks about right
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
01-16-2013, 09:01 PM #5
Professional Member
- Join Date
- Dec 2009
- Posts
- 29
Does the heat exchanger have any holes or cracks in it? As well if your going to replace it I would get a reserver for it as well to prevent it from happening again and if the heat exchanger got replaced I would check if the baffles got removed on installation some require to keep them and some models require you to remove half I'd call carrier to double-check once you figure out if your changing the exchanger or buying the plate for it and reserve.
-
01-16-2013, 09:05 PM #6
What typically causes these burner support plates to fail so soon? See them all the time but sometimes find everything else in line. Give me a carrier like this any day for heat exchanger replacement.
Sent from my SGH-T999 using Tapatalk 2
-
01-16-2013, 09:15 PM #7
Professional Member
- Join Date
- Dec 2009
- Posts
- 29
Top plate rust out cause no one ever orders the reserver plate that goes inside of the 3 or 4 tube passes inside the plate where its all rusted out and the Wholes go big to smaller in size, without it I see heat exchanger replacement every 5 years, its an extra order when you get a new exchanger
-
01-16-2013, 09:16 PM #8
-
01-16-2013, 09:43 PM #9
Carriers and heat exchangers. They go together like sardines and jam.
But Ive even seen Carriers straight from the factory with burner racks installed on an angle causing major flame impingement. I saw that actually cause a premature death on one.
The ones Ive seen this fail on have been the old Carrier units. The lime green deals. The ones we all hope this will happen so we can finally junk the dinosaur haha.Get money, get paid.
-
01-16-2013, 09:51 PM #10
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
[QUOTE=RayD8630;15010391]
But Ive even seen Carriers straight from the factory with burner racks installed on an angle causing major flame impingement.
That might be from the retard forklift idiots.Have you ever looked on the bottom of a unit ? Where the forks end up ?
-
01-16-2013, 10:08 PM #11
-
01-16-2013, 10:12 PM #12
Carriers design is just poop. Lack of post purge and airflow is what kills the heat exchangers. Baffles, NOx plates, blah, blah and blah is not what kills them. Correct your airflow, tune them with an analyzer, and add a 3 min post purge and you will be out of a job.
-
01-16-2013, 10:29 PM #13


Reply With Quote