    heat pump frosted, is it normal

    this morning, around 7am, i turn down my thermostat from 70F to 66F while heat pump compressor was runnung for 5 minutes, then i heard the outdoor unit stop running, and i just happen to walk outside, i saw top and buttom frosted white, middle no frost, is that a sign of leak or low charge? or normal operation? outdoor temperature around 39F at the time, last night it has been running about 16 to 20 minutes per cycle every hour while maintaining indoor at 70F.

    Name:  frosted 1.jpg
Views: 162
Size:  61.9 KBName:  frosted 2.jpg
Views: 112
Size:  61.7 KBName:  frosted 3.jpg
Views: 118
Size:  82.4 KB

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    37,558
    Post Likes
    Depends upon how the system is circuited. Heating uses less refrigerant than cooling and the outdoor coil is way bigger than the indoor coil. In the winter when it is the evaporator, it may not be unusual to see striping like that. Sounds like it is heating the house just fine. 30s especially if humid are the worst frosting conditions.

  3. #3
    Join Date
    Mar 2012
    Posts
    104
    Post Likes
    Name:  frosted 4.jpg
Views: 111
Size:  59.2 KB

  4. #4
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,859
    Post Likes
    Looks like normal operation.

    Frost is normal. Thick ice is not normal.

    Your system will initiate a defrost sequence when the logic board parameters are met.