    Rain or undercharge.
    If there are noncondensibles you will see an un-even frosting pattern across the whole coil.

    ~smoke~
    "That motor's done, he let the factory smoke charge out!"

  2. #22
    Join Date
    Jan 2013
    Posts
    19
    Post Likes
    Thread Starter
    The OAT has not been below 34 & theres been no ice or anything on the house. The unit is on the eve end of the house so forget about water running off the house into it..& r glasgow, the top few rows of the coil are froze really big, not water freezing all across the top of the unit?

  3. #23
    Join Date
    Jan 2013
    Posts
    19
    Post Likes
    Thread Starter
    & if it were non CONDENSEables would that not be in the top of the condenser?? Not causing problems in the evaporator right?

  4. #24
    Join Date
    Jan 2013
    Posts
    19
    Post Likes
    Thread Starter
    Thanks for the input Brent..i'm trying to get my post count up! This is good info but still doesnt explain why it's freezing only at the top..

  5. #25
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    Jmack,

    We can't diagnose the problem for you.

    We can only offer "suggestions." It is very difficult to pinpoint a service issue such as this one from a keyboard.

    You're a technician. Use yours skills, along with info provided and determine the issue. Let us know what you find!

  6. #26
    Join Date
    May 2006
    Location
    Austin, Texas
    Posts
    800
    Post Likes
    Jmack, not sure of that particular coil but refrigerant does not generally enter from one end and exit the opposite end be it top or bottom. The coil has several different circuits. After completely defrosting, run in heat mode with no outdoor fan and observe for frosting pattern. May point you in the right direction.

  7. #27
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Merged your 2 threads. please don't make duplicate threads, thank you.

  8. #28
    Join Date
    Jan 2013
    Posts
    19
    Post Likes
    Thread Starter
    My intentions werent to get a diagnosis. It was simply to discuss the 18 SEER 2 stage system & see if this was "normal". (& get my post count up) Could someone else chime in on the liquid entering the bottom & vapor leaving the top? Thats what all of my text books show & both of my college teachers.

  9. #29
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by JMack13 View Post
    My intentions werent to get a diagnosis. It was simply to discuss the 18 SEER 2 stage system & see if this was "normal". (& get my post count up) Could someone else chime in on the liquid entering the bottom & vapor leaving the top? Thats what all of my text books show & both of my college teachers.
    There are 7 circuits on a 3 ton (may be more on 4 and 5 ton models, haven't counted) and they are evenly spaced top to bottom. So the part that's freezing could be one or two circuits.

    If you open the side panel pull that black plastic sheet out of the way, you can see the vapor manifold and see exactly how the coil is piped.

    I have this unit in my house, the water source version.

  10. #30
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,015
    Post Likes
    It could have several distribution tubes distributing the refrigerant to the different circuits in the outdoor coil. The top one is probably restricted.
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
    http://www.campbellmechanical.com

  11. #31
    Join Date
    Apr 2007
    Location
    Saint Augustine, Florida, United States
    Posts
    1,248
    Post Likes
    run it in ac for a couple hours, the heat will melt the ice. just kidding. it is 75 down here right now.

  12. #32
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Sounds like a restricted distributer tube like air1 said.

  13. #33
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by JMack13 View Post
    My intentions werent to get a diagnosis. It was simply to discuss the 18 SEER 2 stage system & see if this was "normal". (& get my post count up) Could someone else chime in on the liquid entering the bottom & vapor leaving the top? Thats what all of my text books show & both of my college teachers.
    Often text books will show an over simplified example/drawing. Your college teachers are wrong if they think all evap coils are set up with a single feed in the bottom of the coil. It will be multiple circuits with the bottom of each circuit being feed at its bottom.

    You need to look closer at the systems you work on.

  14. #34
    Join Date
    Jan 2013
    Posts
    19
    Post Likes
    Thread Starter
    Thanks guys. I do look at them & i'm still learning every day but ya'll don't understand this small town AL stuff. We might go a year without seeing anything above a 10 SEER!

  15. #35
    Join Date
    Sep 2005
    Posts
    58,704
    Post Likes
    Quote Originally Posted by JMack13 View Post
    Thanks guys. I do look at them & i'm still learning every day but ya'll don't understand this small town AL stuff. We might go a year without seeing anything above a 10 SEER!
    Used to be 75% of what I saw was builder grade... Now I have a customer base that wants better. Takes time to build that base.

    How about filling out your profile with a city/state... then we will know the climate you are in.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  16. #36
    Join Date
    Feb 2012
    Location
    Durham, NC
    Posts
    77
    Post Likes
    The temperature sensors have an ohm reading related to the temp being read. Your trane service manual will have a table to follow for these measurements. Just something worth checking out.

  17. #37
    Join Date
    Nov 2008
    Location
    Piney Flats, Tn.
    Posts
    2,282
    Post Likes
    10 seer or 18 seer Trane or Goodman all are designed similar meaning all circuits are very much the same maybe 4 to 9 inches in height on a cond. coil and as stated has many and the size dictates how many circuits, evap coil not the same but has several circuits maybe 2 circuits per ton. any one circuit could be restricted we and you can not tell over the phone or computer. so just because it is an 18 seer it is still a normal heat pump circuit refrigerant circuit and defrost the same.

    dogboy

  18. #38
    Join Date
    Mar 2004
    Location
    Chester County PA
    Posts
    588
    Post Likes
    Maybe it's only running single stage and never ramps up.
    When I find a heat pump with half, or less, of the outdoor coil frozen solid it usually means under charged. If it's a 2 stage heat pump maybe it never comes out of 1st stage
    "That motor's done, he let the factory smoke charge out!"

  19. #39
    Join Date
    Mar 2002
    Posts
    522
    Post Likes
    Check subcooling. I would guess either low subcooling and the top circuit not getting a solid flow of liquid or a restriction in the top circuit.

  20. #40
    Join Date
    Jan 2013
    Posts
    19
    Post Likes
    Thread Starter
    Solid flow of liquid in the top of the evaporator?...

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •