Thread: Help! American Standard 18SEER
-
01-16-2013, 09:51 PM #27
Merged your 2 threads. please don't make duplicate threads, thank you.
-
01-16-2013, 10:33 PM #28
Regular Guest
- Join Date
- Jan 2013
- Posts
- 19
My intentions werent to get a diagnosis. It was simply to discuss the 18 SEER 2 stage system & see if this was "normal". (& get my post count up) Could someone else chime in on the liquid entering the bottom & vapor leaving the top? Thats what all of my text books show & both of my college teachers.
-
01-16-2013, 11:06 PM #29
There are 7 circuits on a 3 ton (may be more on 4 and 5 ton models, haven't counted) and they are evenly spaced top to bottom. So the part that's freezing could be one or two circuits.
If you open the side panel pull that black plastic sheet out of the way, you can see the vapor manifold and see exactly how the coil is piped.
I have this unit in my house, the water source version.
-
01-16-2013, 11:17 PM #30
It could have several distribution tubes distributing the refrigerant to the different circuits in the outdoor coil. The top one is probably restricted.
"The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
"Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
"Beer is living proof that God loves us and wants us to be happy" --Benjamin Franklin
-
01-16-2013, 11:25 PM #31
run it in ac for a couple hours, the heat will melt the ice. just kidding. it is 75 down here right now.

-
01-17-2013, 12:49 AM #32
Sounds like a restricted distributer tube like air1 said.
-
01-17-2013, 05:43 AM #33
Often text books will show an over simplified example/drawing. Your college teachers are wrong if they think all evap coils are set up with a single feed in the bottom of the coil. It will be multiple circuits with the bottom of each circuit being feed at its bottom.
You need to look closer at the systems you work on.
-
01-17-2013, 08:03 AM #34
Regular Guest
- Join Date
- Jan 2013
- Posts
- 19
Thanks guys. I do look at them & i'm still learning every day but ya'll don't understand this small town AL stuff. We might go a year without seeing anything above a 10 SEER!
-
01-17-2013, 04:32 PM #35
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,298
GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.
-
01-17-2013, 06:23 PM #36
Professional Member
- Join Date
- Feb 2012
- Location
- Durham, NC
- Posts
- 64
The temperature sensors have an ohm reading related to the temp being read. Your trane service manual will have a table to follow for these measurements. Just something worth checking out.
-
01-18-2013, 09:20 AM #37
10 seer or 18 seer Trane or Goodman all are designed similar meaning all circuits are very much the same maybe 4 to 9 inches in height on a cond. coil and as stated has many and the size dictates how many circuits, evap coil not the same but has several circuits maybe 2 circuits per ton. any one circuit could be restricted we and you can not tell over the phone or computer. so just because it is an 18 seer it is still a normal heat pump circuit refrigerant circuit and defrost the same.
dogboy
-
01-18-2013, 06:31 PM #38
Professional Member*
- Join Date
- Mar 2004
- Location
- Chester County PA
- Posts
- 285
Maybe it's only running single stage and never ramps up.
When I find a heat pump with half, or less, of the outdoor coil frozen solid it usually means under charged. If it's a 2 stage heat pump maybe it never comes out of 1st stage"That motor's done, he let the factory smoke charge out!"
-
01-19-2013, 01:24 AM #39
Professional Member
- Join Date
- Mar 2002
- Posts
- 516
Check subcooling. I would guess either low subcooling and the top circuit not getting a solid flow of liquid or a restriction in the top circuit.