Results 1 to 13 of 107
01-15-2013, 08:25 PM #1
- Jan 2013
- San Gabriel Valley, California
- 32
FengsHVAC a Professional HVAC Tech teach you how to fix the heat on Bryant Pkg Unit
Problem: heat pump produce no heat, only blow cold air.
Insight: Called for heat, Blower ran, but compressor didn't come on.
Cause: dirty air filter cause the high pressure switch to trip during heat mode.
Solution: While it was calling for heat, checked 24v on the Y wire from the thermostat at the unit, got 24v. checked 24v at the compressor contactor coil, no voltage. found High pressure swith is in between, reset it. cleaned the air filter, turned the heat back on.
01-15-2013, 08:52 PM #2
Moved to tech to tech commercial
01-15-2013, 09:44 PM #3
Teach us more, all knowing and wise Fengmaster...
Was the reversing valve energized while you had 24v at Y?
01-15-2013, 11:09 PM #4
- Feb 2012
- EVERYWHERE
- 161
And now it's time for HVAC talk with FengsHVAC.
01-16-2013, 12:27 AM #5
- Jan 2013
- 32
01-16-2013, 06:16 AM #6
wow...heat pump class
01-16-2013, 07:19 AM #7
Check the filter class.....
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
01-16-2013, 08:12 AM #8
You better fix that refer leak below the HPS.
change a filter, Fix a heat pump.Certified parts changer.
01-16-2013, 08:15 AM #9
I long to be as technically proficient as the OP.
01-16-2013, 08:17 AM #10
01-16-2013, 08:19 AM #11
01-16-2013, 08:37 AM #12
Professional Member*
- Dec 2002
- SouthEast NC ICW & Piedmont Foothills
- 7,215
01-16-2013, 09:29 AM #13