    Gem three-door reach-in freezer - how many HP?

    Someone stole the condensing unit for this Gem three-door freezer. Three 30" doors. What HP condensing unit would you think it requires? The owner claims there is no model number on it.

    PHM
    ------
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    5,616
    wild ass guess would be 1 HP. I'll look at some old books when i get to work.

  3. #3
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,328
    I agree with 1 HP if it has solid doors. Glass doors would require a 1 1/2 HP like a KATB-015E-CAV.

  4. #4
    Join Date
    Sep 2002
    Posts
    12,282
    I forgot the doors - they are glass: display doors.

    Good thing I asked you - the owner said that he thought it had been 3 HP - which seems high to me - but I was still guessing 2 HP. <g>

    But 1 1/2 HP will do it huh?

    PHM
    ------





    Quote Originally Posted by icemeister View Post
    I agree with 1 HP if it has solid doors. Glass doors would require a 1 1/2 HP like a KATB-015E-CAV.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  5. #5
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,328
    I was going by memory and what is currently used in 3-door reach-ins.

    I do recall working with a 3-door Pinnacle however, which had a 2 HP EAV2-0200.

  6. #6
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,163
    say you oversized it by 1/2 hp , what might that do ....

    pros cons

  7. #7
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,328
    Quote Originally Posted by Snapperhead View Post
    say you oversized it by 1/2 hp , what might that do ....

    pros cons
    As long as the TXV (or the cap tube) is properly sized for the condensing unit capacity there should be no problem going up one size. It'll run a slightly lower evap temp and be able to hold a lower box temp. Supermarket cases do this all the time with essentially the same case for either frozen foods or ice cream. the ice cream just requires a bigger unit to hold the lower temps.

    Actually, in PHM's case, the 2 HP unit may be the prudent approach. I found some old literature for a couple of other 3-door display freezers which called for 2 HP units.