Results 1 to 13 of 13
  1. #1
    Join Date
    Jan 2009
    Location
    Clemson, SC
    Posts
    23

    Confused Got one driving me crazy

    Ok here it goes... I got one driving me crazy.This is a heatpump. In a dentist office the hyg. area the grils are turning on the heat in the morning then turning on the ac when in the afternoon. They call me in the afternoon and say the ac is not working. I changed out the compressor about a month ago and sometimes when I go to check it out the pressures look great. But the compressor is tripped out on hi temp. or tripping the breaker. I went out yesterday and replaced the dryer filter. Pulled a new vac and got the pressures set. For sh** and giggles I pulled the guages off and connected to the unit beside the one I was working on to verify the pressures and both were the same. Any suggestions on what the problem could be?

  2. #2
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,456
    Maybe a floating restriction. But, the tripping the breaker doesn't make sense. How's the fan motors? Any side to side play? wiring look good? Check run cap on compressor too. Especially, if it has a start assist.

  3. #3
    Join Date
    Jan 2013
    Location
    Texas
    Posts
    31
    Have you checked your high volt lines for a skinned wire or short of some sort? possible loose connection/grounding wire on the high volt possibly?

  4. #4
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    926
    Not enough information here to be of any help. What did you check? Did you cycle the reversing valve and check in both heat and cool? Amp draws and voltages? Are you weighing the charge in?
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin

    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain

    "Beer is living proof that God loves us and wants us to be happy" --Benjamin Franklin

  5. #5
    I had a 410-A split-A/C once where the condenser was on the ground and the coil on the third floor. Pressures looked great for the first 10-15 minutes of run time, then the head would start to steadily climb until the bypass opened. Whole problem was just overcharge. Just a thought.

    -Brian

  6. #6
    Join Date
    Jan 2013
    Posts
    19
    What was the reason for changing the dryer?

  7. #7
    Join Date
    May 2011
    Posts
    79
    If I had a tripped breaker, I'd have immediately checked the cap just to rule it out.

  8. #8
    Join Date
    Oct 2007
    Location
    Maine
    Posts
    11
    It seems you are saying it works in the morning in heat mode and not in the afternoon when calling for cooling. Sounds like it might be a reversing valve issue.

  9. #9
    Join Date
    May 2009
    Location
    Savannah, Ga/H.H. Island, S.C.
    Posts
    741
    Check your condenser coil. Make sure you have a clean coil. Also, make sure you have plenty of clearance for the condenser to get proper air circulation.

  10. #10
    Join Date
    May 2006
    Location
    Austin, Texas
    Posts
    185
    Don't know which heatpump you have but if heats in morning and want cool in afternoon; look for high head pressures. Could be simply dirty filters. During heating the compressor trips breaker and auxiliary heat keeps the office warm. Turn on cooling and nothing. They call you.

  11. #11
    Join Date
    Dec 2010
    Location
    Downingtown, PA
    Posts
    5
    Heat pumps are strange animals. Does your condenser have a low ambient kit? If so, did you verify that it's cycling on and off correctly. I would also look at reversing valve and defrost cycle.

  12. #12
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    4,437
    All these responses and no one asked the obvious.

    Recip compressor with indoor txv in cooling with no start kit.

  13. #13
    Join Date
    May 2009
    Location
    Savannah, Ga/H.H. Island, S.C.
    Posts
    741
    Sb might be onto something. Please post model and serial of unit for both the HP and AHU.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •