Results 14 to 25 of 25
Thread: First New furace/ac install
-
01-15-2013, 07:46 PM #14
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
Why hard pipe on the suction ?
-
01-15-2013, 07:50 PM #15
Professional Member*
- Join Date
- Jul 2001
- Location
- Anderson,SC
- Posts
- 882
Sounds good to me,good luck.
Stud
-
01-15-2013, 10:55 PM #16
Looks nice
sent from my kindle fire using tapatalk 2 please excuse any typographical errors using tapatalkIf you can not do it right, Why even do it at all?
-
01-17-2013, 01:03 PM #17
Very nice. May regret not running the lineset along the wall and 90 straight out to unit.
-
01-19-2013, 08:03 PM #18
Why is the overflow on the evapoartor coil not piped in?
What happens to the water when the primary drain plugs up?
-
01-20-2013, 01:02 PM #19
Regular Guest
- Join Date
- Jul 2012
- Location
- Cincinnati ohio
- Posts
- 101
-
01-20-2013, 02:00 PM #20
On up-flow units we install a safety switch. It's code.
I don't want to hear you complaining!
-
01-20-2013, 02:22 PM #21
Regular Guest
- Join Date
- Sep 2012
- Posts
- 7
-
01-20-2013, 08:07 PM #22
-
01-20-2013, 08:20 PM #23
Professional Member
- Join Date
- Nov 2011
- Location
- Charleston, Wv.
- Posts
- 681
I would have 90'd from the building rather than 45'd....personal preference really....less line hanging in the open. also don't see a point in rigid on the SL.
are you saying the combustion condensate was internally trapped, or the coil is internally trapped?
I also would have shortened the 'T' and capped it on the drain line. shouldn't be any issues unless static is high.
also snow legs on the furnace to keep the metal off the concrete (if you have the room), and the same on cond. keeps both from rusting early, and allows cond. to drain without getting crap plugging up the drains.
overall nice job though!
-
01-20-2013, 09:13 PM #24
Ive been to a few calls were the overflowed water got into the furnace control board....water and control board bad marriage
-
01-20-2013, 11:15 PM #25
Professional Member
- Join Date
- Jun 2009
- Location
- Ontario, Canada
- Posts
- 846
dont need a trap, it's under positive pressure... but it does need atmospheric vent