Page 2 of 2 FirstFirst 12
Results 14 to 18 of 18
  1. #14
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,131
    Sounds like they may be getting to the root of the problem. Youll find that outside of setbacks than, you probably dont even need more than low stage other than for a few hours on the coldest days.


    Sent from my SGPT12 using Tapatalk 2

  2. #15
    Join Date
    Apr 2012
    Posts
    9

    Cool

    IT'S FIXED!!!!!!!!!!!!!!!!

    On Saturday, they installed a new limit switch. Got a system malfunction on Sunday, early morning. I lowered the thermostat to 68 so as to not stress the furnance and the new limit switch.

    On Wednesday, they replaced the blower motor. BINGO. Everything works great now. The temperature inside the furnace on max heat via probe reading is around 155 and that's with the humidifier bypass damper open and the new vent that was installed just above the A/C coil for heat relief completely closed. Static pressure is now 0.61.

    I am so happy its working finally. Thanks to everyone here who read and responded to my saga. Having additional input on the situation really helped.

  3. #16
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    2,270
    Quote Originally Posted by joeWI View Post
    IT'S FIXED!!!!!!!!!!!!!!!!

    On Saturday, they installed a new limit switch. Got a system malfunction on Sunday, early morning. I lowered the thermostat to 68 so as to not stress the furnance and the new limit switch.

    On Wednesday, they replaced the blower motor. BINGO. Everything works great now. The temperature inside the furnace on max heat via probe reading is around 155 and that's with the humidifier bypass damper open and the new vent that was installed just above the A/C coil for heat relief completely closed. Static pressure is now 0.61.

    I am so happy its working finally. Thanks to everyone here who read and responded to my saga. Having additional input on the situation really helped.
    I still wouldn't be happy. The temp rise for that furnace is 35 to 65 degrees. so even at 70 indoor the max outlet temp should be 135.
    It's not the Brand with the fewest repairs-It's all in the install!!! Attention to detail and using the best materials!

  4. #17
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,131
    I wonder if the bypass humidifier is bypassing too much air. On some you can adjust the damper to reduce flow. I agree that 135F should be max. Something still doesn't seem right. Gas pressure/Overfired?

  5. #18
    Join Date
    Feb 2010
    Location
    butler pa
    Posts
    1,058
    Quote Originally Posted by motoguy128 View Post
    Gas pressure/Overfired?
    sounds a bit too toasty warm..think on the carriers ya gotta adj high first,then med,then low. havent played w one of the 3 stage infinitys..

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •