Trane YCD036D manual?
Does anyone have a link to the maintenance manual for the YCD series RTU? I'm having a hell of a time finding anything online.
Any useful Trane troubleshooting guides would be helpful......
-
01-15-2013, 08:40 AM #2
Professional Member
- Join Date
- May 2010
- Location
- Canada
- Posts
- 289
I'm just trying to get a copy of the book that comes with the unit and can find anything at all online. The stat is flashing "E1" which is heating failure. The unit wont fire ( combustion motor wont even start ) in test mode. I only had a couple minutes last night to troubleshoot because they were closing. The unit had no book or wiring diagram ( none of the units did ). I quickly changed out the relay and ignition control board with a unit that was working and still no go.
-
01-15-2013, 09:49 AM #3
Did you check for voltage at the motor?
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
01-15-2013, 10:11 AM #4
Regular Guest
- Join Date
- Oct 2007
- Location
- Maine
- Posts
- 11
If there is voltage at the motor try to give it a spin. Sometimes these ones freeze in place.
-
01-15-2013, 12:04 PM #5
Professional Member
- Join Date
- May 2010
- Location
- Canada
- Posts
- 289
Ok so here is what Happened. My ampmeter was reading ohms, capacitance, and amps but had failed on voltage. There was voltage to the motor but my meter let me down.
Thanks for the help.
-